Clearance to Storage with In-Rack Sprinklers for Group A Plastics



You have asked the following questions: “I have a project with storage of 
exposed, unexpanded Group A plastics in racks to a height of 20 ft with a 
building height of 40 ft 7 in. Is Section 12.1.3.4.8 requiring an acceptable 
clearance from storage to the ceiling with in-rack sprinklers or does it remove 
the acceptable clearance requirement from storage to the ceiling if in-rack 
sprinklers are installed? If I were to install in-rack sprinklers per Section 
12.1.3.4.8 would I be able to use any of the rack configurations described in 
Section 17.2.1.4? For example, I could use any of the rack options for 20 ft of 
storage in a 25 ft building or 20 ft of storage in a 30 ft building? Also, 
Figure 17.2.1.4(j) shows a line of sprinklers directly over the top level of 
storage. Would this configuration require a solid barrier above the top of the 
storage?” In response to your question, we have reviewed NFPA 13, 2013 edition 
as the applicable standard. Our informal interpretation is the Section 
12.1.3.4.8 negates the excessive clearance.

There are multiple sections that have to be referenced when you determine a 
design criteria and when the acceptable clearance between the top of the 
storage and ceiling is exceeded. The main section to review is Section 12.1.3, 
which covers the requirements pertaining to storage height and building height. 
Section 12.1.3.3 requires the design to be based off of the storage 
configuration that routinely or periodically is found in the building requiring 
the greatest water demand. The clearance from storage to ceiling requirements 
are contained in Section 12.1.3.4. Then Section 12.1.3.4.2 states: “for spray 
sprinkler criteria where the clearance to ceiling exceeds those identified in 
this section, the requirements of 12.1.3.4.3 through 12.1.3.4.8 shall apply.” 
Since the term “through” is used every applicable part of those sections have 
to be adhered to. With the storage commodity being exposed, unexpanded Group A 
plastics stored to a height of 20 ft. Section 17.2 contains the design 
requirements. Thus Sections 12.1.3.4.5, 12.1.3.4.7, and
12.1.3.4.8 are applicable. Section 12.1.3.4.5 requires the protection criteria 
to be determined by using a storage height that would result in clearance to 
the ceiling of 10 ft. or install a supplemental row of in-rack sprinklers. For 
example, use the design requirements for storage height of 31 ft for a building 
height of 40 ft 7 in. even if the storage height is only 20 ft. An equally 
acceptable approach is to install one level of supplemental, quick-response 
in-rack sprinklers located directly below the top tier of storage at every flue 
space intersection to be provided instead. Then Section 12.1.3.4.7 in 
conjunction with the supplemental in-rack sprinklers dictates the ceiling 
density to be based upon the given storage height as if the acceptable 
clearance to the ceiling were met. In other words, the supplemental in-rack 
sprinklers negates the excessive clearance. Next, Section 12.1.3.4.8 states if 
the design criteria already requires in-rack sprinklers for a certain storage 
configuration, provide those in-rack sprinklers as well as the supplemental 
in-rack sprinklers required by Section 12.1.3.4.5. After reviewing Figure 
17.2.1.4(j) it is believed the line of sprinklers shown above the top level of 
storage is an error (effectively a typo) and those sprinklers are to be 
installed directly below the top tier of storage. This is supported by the 
configuration in the 2019 edition being shown without the sprinkler above the 
top tier (Figures 25.9.3.3(g) and 25.9.3.3(i)).