sprinklernotes
Sprinkler Protection in Decorative Cupolas


You have asked the following question: “Is there a section in NFPA 13 that will 
allow a sprinkler to be omitted from a cupola which is built on top of a roof 
as a decorative feature? There is no penetration between the roof and the 
cupola. Inside the cupola, there will be a window and light at the top. The 
exterior dimension of the base is approximately 8 ft. by 8 ft. but narrows to 4 
ft. by 4 ft. before the top and is approximately 11 ft. tall. The cupola will 
be subject to freezing temperature, requiring a dry system to be installed for 
a single sprinkler if sprinkler protection is required.” In response to your 
question, we have reviewed NFPA 13, 2016 edition as the applicable standard. 
Our informal interpretation is sprinkler protection is required.

In this situation, it is important to keep in mind the purpose of installing 
sprinklers per NFPA 13. The purpose is stated in Section 1.2.1:
The purpose of this standard shall be to provide a reasonable degree of 
protection for life and property from fire through standardization of design, 
installation, and testing requirements for sprinkler systems, including private 
fire service mains, based on sound engineering principles, test data, and field 
experience.
With this purpose in mind, the requirements for protecting the cupola can be 
reviewed.

The first section to review for this situation is Section 8.15.1.2.18.1, which 
states:

Sprinklers shall be permitted to be omitted from within combustible soffits, 
eaves, overhangs, and decorative frame elements that are constructed in 
accordance with 8.15.1.2.18.2 through 8.15.1.2.18.5.

Since Section 8.15.1.2.18.1 states “8.15.1.2.18.2 through 8.15.1.2.18.5” all 
four conditions listed have to be met. With the cupola being on top of the roof 
structure Section 8.15.1.2.18.2 does not apply because the 4-ft maximum width 
in Section 8.15.1.2.18.2 is directed at limiting the impact of combustibles 
beneath overhang type features. With that being said, this allowance is not 
limited to just features on the exterior wall such as overhangs. It also 
applies to features on the roof, as indicated by Section 8.15.1.2.18.4 
dictating separation by walls or roofs of noncombustible construction. Next, 
Section 8.15.1.2.18.3 is requiring the cupola to be less than 160 cu. ft., 
which it is not. Since the cupola does not meet Section 8.15.1.2.18.3, this 
alone removes the possibility of applying Section 8.15.1.2.18.1 to omit 
sprinkler protection. Continuing on to Section 8.15.1.2.18.4, the cupola is 
required to be separated from the main building interior by walls or roofs of 
noncombustible or limited-combustible construction. To be considered 
noncombustible or limited-combustible the structural members have to be 
noncombustible along with the exposed finish material. If the any portion of 
the roof structure is combustible then Section 8.15.1.2.18.4 also removes the 
possibility of applying Section 8.15.1.2.18.1 (to omit sprinkler protection). 
Finally, Section 8.15.1.2.18.4 requires no openings or unprotected penetrations 
directly into the building, which there are none. As stated, all of the 
conditions listed in Section 8.15.1.2.18.1must be met to omit sprinkler 
protection and not all of the four are not met in this situation, thus 
sprinkler protection is required in the structures.

However, the purpose of “to provide a reasonable degree of protection for life 
and property from fire” “based on sound engineering principles, test data, and 
field experience” can be achieved through other means. NFPA 13 states this in 
Section 1.5:

Nothing in this standard is intended to prevent the use of systems, methods, or 
devices of equivalent or superior quality, strength, fire resistance, 
effectiveness, durability, and safety over those prescribed by this standard.

This allows the designer and AHJ the flexibility to use other protection 
methods than those prescribed by NFPA 13 as long as the protection methods 
proposed do not decrease the level of safety required by NFPA 13. This supports 
the overall purpose of NFPA 13. In this situation, it could be argued 
installing a heat and/or smoke detector within the cupola would provide a 
similar level of life safety since the cupola is only for decorative purposes. 
If a fire were to start within the cupola and activate the detector it would 
allow for the occupants to evacuate and the fire department to respond before 
progressing into the main structure. This protection method would have to be 
discussed with the local AHJ and a written agreement with this protection 
method shall be obtained before proceeding further with the project per Section 
1.5.2, which states:
The system, method, or device shall be approved for the intended purpose by the 
authority having jurisdiction.
This protection method would allow for omission of the sprinkler within the 
cupola while still meeting the level of life safety required by NFPA 13.