sprinklernotes
Fire Pump Test Header Supply Pipe Sizing


You have asked the following question: “When sizing the piping to the test 
header, am I allowed to reduce down to a 4 in. pipe to go through the wall if 
Table 4.27 requires an 8 in. pipe to supply the test header?” In response to 
your question, we have reviewed NFPA 20, 2016 edition as the applicable 
standard. Our informal interpretation is hose valve header supply pipes are 
allowed to be sized by hydraulic calculations based on a total flow of 150 
percent of rated pump capacity.

The requirement for sizing test header (hose valve headers) supply pipes are 
located in Section 4.21.3.1.3, which states:
Where outlets are being utilized as a means to test the fire pump in accordance 
with 4.21.1.1, one of the following methods shall be used:
(1) Hose valves mounted on a hose valve header with supply pipe sized in 
accordance with 4.21.3.4 and Section 4.27
Section 4.21.3.4 allow one of two methods to be used when determining the pipe 
size. The most applicable method in this situation is the second option 
provided, which is:
This pipe is permitted to be sized by hydraulic calculations based on a total 
flow of 150 percent of rated pump capacity, including the following:
(a) This calculation shall include friction loss for the total length of pipe 
plus equivalent lengths of fittings, control valve, and hose valves, plus 
elevation loss, from the pump discharge flange to the hose valve outlets.
(b) The installation shall be proven by a test flowing the maximum water 
available.
This allows the piping to be sized per hydraulic calculations. However, Section 
4.21.3.1.3 requires test headers supply pipes to meet both Sections 4.21.3.4 
and 4.27. Section 4.27 states:
The sizes indicated in Table 4.27(a) and Table 4.27(b) shall be used as a 
minimum.
This requires the sizes listed in Table 4.27 to used as a minimum, which 
appears to be in conflict with Section 4.21.3.4. However, Note 4 of Table 4.27 
test headers to be size per Section 4.21.3.4. Note 4 of Table 4.27 states:
The hose header supply is permitted to be sized in accordance with 4.21.3.4.
Thus, as long as hydraulic calculations support reducing a portion of the test 
head supply pipe from 8 in. to 4 in. and proven by a flow test after 
installation, it is an acceptable installation.

Reply via email to