sprinklernotes

Concealed Spaces and Special Sprinklers

 

 

 

You have asked the following question: “We have a four-story hotel with open 
web wood trusses spaced 1 ft. 6 in on center at the roof. The top chord of the 
truss is 2 by 6 (on edge) with 2 by 4 (on edge) web members and bottom chord. 
Overall truss height is 30 in. to 38 in. and they are 32 ft. 6¾ in. in length. 
When calculating the percentage of the opening to determine if the space is 
obstructed construction, is it necessary to take the dimension of the top chord 
into consideration if the deflector is located below the top chord? If the 
cross-sectional area is not 70 percent open, are sprinklers required in between 
each bay? Are special combustible concealed space sprinklers required for part 
or all of the combustible space?” In response to your question, we have 
reviewed NFPA 13, 2016 edition as the applicable standard. Our informal 
interpretations are explained below.

 

Let’s take the questions in the order they were asked. The top chord must be 
included in the determination of how much of the cross-sectional area is open. 
The location of the sprinkler does not impact this issue since it is all about 
heat flow along the ceiling. The dimensions of the top cord of the truss in 
this application is critical when determining if the construction is considered 
obstructed or unobstructed. If the depth is greater than 4 in., NFPA 13 
considers this to be obstructed construction. This is stated in Sections 
A.3.7.1(8) and (9). Section A.3.7.1 provides examples of what NFPA 13 considers 
to be obstructed construction. Then A.3.7.1(9) states: Truss Construction (Wood 
or Steel). The term truss construction refers to parallel or pitched chord 
members connected by open web members supporting a roof or floor deck with top 
and bottom members greater than 4 in. (100 mm) in depth.

 

As for the second question, there is no direct requirement to place the 
sprinklers in every bay (also called a channel NFPA 13) for obstructed 
construction, as required for ESFR sprinklers. What does drive the issue is 
allowed distance below the ceiling and the ability to comply with the 
obstruction rules. If the truss assemblies were considered obstructed 
construction, then sprinklers have to be put into every channel since the beam 
rule can’t meet. If the truss is at least 70 percent open, measure the 6 in. 
below the structural member to the bottom of the top chord and then try to meet 
the three times rule required by the obstruction criteria. This is a challenge 
with closely spaced trusses. Due to the truss’ dimensions and the spacing 
between truss the options are limited within Section 8.6.5.2.1. The only real 
option that would be applicable is Section 8.6.5.2.1.7, which states:

 

Sprinklers shall be permitted to be installed on the centerline of a truss or 
bar joist or directly above a beam, provided that the truss chord or beam 
dimension is not more than 8 in. (200 mm) and the sprinkler deflector is 
located at least 6 in. (150 mm) above the structural member and where the 
sprinkler is positioned at a distance three times greater than the maximum 
dimension of the web members away from the web members.

 

This too is likely a challenge which could require installing sprinklers in 
every channel.

 

Next, Section 8.15.1.6 needs to be reviewed due to the lack of space from deck 
to deck for the spray pattern of a standard sprinkler to fully develop. Section 
8.15.1.6 requires sprinklers that are specifically listed for use in concealed 
spaces to be installed in concealed spaces that meet all of the following three 
conditions; a horizontal concealed space (slope no more than 2 in 12), a 
combustible upper surface, and a depth of no more than 36 in. Since this is 
Type V, it is assumed it has an upper wood surface and that it is exposed. If 
the upper surface is covered in insulation, the interpretation is the upper 
surface is not exposed so a sprinkler that is specifically listed concealed 
spaces would not be required. Since this concealed space has portions that have 
a depth of 30 to 38 in., concealed space sprinklers are required. Then Section 
8.15.1.6.2 allows those special concealed space sprinklers to be installed 
throughout a concealed space that has portions which may exceed a depth of 36 
in. Thus, the areas having a depth greater than 36 in. to 38 in. can use the 
concealed space sprinklers as well.