sprinklernotes

Design Areas and the 30% Increase Requirements

You asked the following questions: “We have a space similar to the space 
described in section 8.15.1.2.16 and A.8.15.1.2.16, and the space above the 
insulation is an unheated unoccupied wood truss space with a slope greater than 
2/12. Using the Density/Area Method the resulting Density/Area would begin with 
0.1 at 1,500 per 11.2.3.1.1. The design area would be increased by 30 percent 
per 11.2.3.2.4 and 11.2.3.2.5 resulting in a Density/Area of 0.1 at 2,535. And 
lastly section 11.2.3.2.7.2 would be applied and the final resulting 
Density/Area will be 0.1 at 3,000. Is this the correct process to developing 
the Density/Area for the space above the insulation?” In response to your 
question, we have reviewed NFPA 13, 2007 and 2016 editions as the applicable 
standard. Our informal interpretation is you have asked multiple questions 
which are answered below.

To answer your first question, you would have to apply Section 11.2.3.2.4 which 
tells us for roof slopes that exceed a 2 in 12 pitch you would have to increase 
your design area by 30 percent from 1500 sq. ft. to 1950 sq. ft. The reasoning 
for the design area increase for sloped ceilings is that the heat from a fire 
is likely to activate sprinklers outside the fire area as the heat travels to 
the high point on the roof which could overwhelm the sprinkler system. This was 
proven in fire tests conducted by FM Global which was the justification for 
Section 11.2.3.2.4 to be added to the standard by the technical committee. 
Additionally, since you stated the area is unheated Section 11.2.3.2.5 applies 
which is another design area size increase for using dry systems resulting in 
an area of 2,535 sq. ft. Again, this design area increase is due to the 
potential for the fire to increase in size due to the delay in water being 
discharged from the sprinklers that have activated.

The final question is does Section 11.2.3.2.7.2 tells us to now apply the 3,000 
sq. ft.- minimum size due to the area below the insulation not being protected? 
This is indeed the correct process when an attic-type space has an unprotected 
concealed space adjacent to it. The primary question though, is the area 
beneath the insulation considered a combustible concealed space? If you go back 
to the original proposal that created this criterion (ROP A2006: proposal 
13-288), it states the only combustibles in the space are the bottom of the 
chords and the insulation facing. Unfortunately noting in the text states this 
except for the restriction on the insulation facing to a heat content of no 
more than 1,000 btu/sq. ft. This is an existing allowance where a concealed 
space is treated as noncombustible even when there is combustible insulation 
facing with this maximum heat content. So, as long as the area beneath the 
insulation is otherwise noncombustible, sprinklers can be omitted without 
triggering the 3,000 sq. ft. remote area requirement by Section 11.2.3.1.4.

Reply via email to