Supporting Multiple Pipes from a Single Trapeze Hanger Assembly

You have asked the following question: “I want to use a single trapeze member 
to support multiple mains. Section A.9.1.1.7 says that the required section 
modulus can be added to determine the trapeze size. This section does not 
mention any limit. I would like to use a 2½ in. by 2½ in. by 3/16 in. angle 
spanning four feet to support two 6-inch mains, a 4-inch main, a 2½-inch main 
and a 2-inch main. Is it the intent of NFPA 13 to allow the addition of the 
required section modulus with no limit as to how many mains can be supported as 
long as the available section modulus is not exceeded? In addition, Section 
9.1.1.7.5 says that all components shall be sized to support the suspended 
sprinkler pipe. So, with the above scenario, would ½inch rod attaching the 
trapeze to the structure meet the requirements of NFPA 13 for trapeze hangers 
per Table 9.1.2.1? It would seem that if a trapeze was utilized to support 
multiple 6-inch mains that the attachments to the structure would need to be 
larger than ½-inch?” In response to your question, we have reviewed NFPA 13, 
2016 edition as the applicable standard. Our informal interpretation is the 
responses to the multiple questions are below.

It is the intent of Section A.9.1.1.7 to allow the addition of the required 
section modulus with no limit as to how many mains can be supported as long as 
the available section modulus is not exceeded. However, Section A.9.1.1.7 is 
located within Annex A, thus is not a requirement within NFPA 13. The 
information provided within Annex A is a recommendation or explanatory 
material. With this in mind this topic should be discussed with the local AHJ 
and a written agreement with this interpretation should be obtained (or at 
least an email sent to the AHJ identifying the outcome of the discussion) 
before proceeding further with the project.

To further complicate the matter, Table 9.1.2.1 only provides hanger rod sizes 
for a single pipe up to 12 in. in diameter. There is no information provided in 
Annex A for Section 9.1.2.1 or Table 9.1.2.1 for what to do when multiple pipes 
are supported by one hanger assembly. With this being the case one can assume 
that multiple pipes up to an equivalent diameter of those listed in Table 
9.1.2.1 can be hung using the hanger rode sizes listed in Table 9.1.2.1. This 
limits hanger assemblies to one 12 in. pipe or multiple pipes that are 
equivalent up to one 12 in. pipe. Keep in mind that Section 9.1.2.2 allows 
hanger rods of smaller diameter than listed in Table 9.1.2.1 to be used when a 
hanger assembly has been tested and listed by a testing laboratory and 
installed per the listing of the hanger assembly.