sprinklernotes

Combustible Canopies not Accessible from Within Dwelling Units

You asked the following questions: “We have a Construction Type V building that 
falls under NFPA 13R where there is a large common area in the center and two 
wings, left and right for residential units. There is a large combustible 
canopy at the front entrance, a large combustible canopy at the rear entrance, 
and two small combustible canopies at the end of each wing serving a corridor 
and not dwelling units, are sprinklers required in these canopies? Does Section 
6.6.5.1 apply?” In response to your question, we have reviewed NFPA 13R, 2016 
edition as the applicable standard. Our informal interpretation is sprinkler 
protection is not required.

There is a definite distinction between the two different types of exterior 
construction features. NFPA 13R section 6.6.5.1 states: Where a roof or deck is 
provided above, sprinklers shall be installed to protect attached exterior 
balconies, attached exterior decks, and ground floor patios serving dwelling 
units in buildings of Construction Type V. This requirement was added to the 
2013 edition but not because the committee agreed with it, since they had 
opposed it (with good reasons) for several cycles. It was added because the 
International Building Code has required it for many years and NFPA 13R needed 
to correlate with the building code. Its objective is to reduce the potential 
for fires to extend up the side of the building from balcony to balcony and 
extend into the attic. As such, it is definitely dependent on the type of 
construction and applies just to Type V (combustible) construction. Two 
critical points are clarified by the Automatic Sprinkler System for Residential 
Occupancies. These are: This rule applies to the exterior or open spaces 
accessible only from the dwelling unit itself and not a corridor or breezeway 
that is shared among multiple dwelling units. This section also is explicit in 
that if there is not a roof or deck above the balcony or porch, no protection 
is required—a balcony under an eave with a soffit or fascia board would not be 
mandated to have sprinklers added. Since the entry canopies are serving the 
entry points of the buildings (no dwelling units), it is not subject to this 
requirement. The other locations identified in section 6.6.5, despite having 
ceiling/roofs, do not require protection.

In closing, section 6.6.5 would apply to your situation and sprinkler 
protection is not required in the attached canopies at the multiple locations 
described in your question.