sprinklernotes
NFPA 13D and Sprinkler Protection in Open and Attached Patios

 

 

 

You have asked the following question: “We have been required to install dry 
pendent sprinklers over an outdoor gas grill and a separate fireplace in an 
outdoor living area on the first floor of a 13D installation. The AHJ is 
requiring the sprinkler per NFPA 13D Section 8.3.5.1.2. We calculated these 
sprinklers at a 0.05 gpm/ft density in accordance with Section 10.1.1.1. The 
calculations were rejected during plan review because we did not calculate 
these two sprinklers at a 0.1 gpm/ft density. The section being referenced for 
this requirement was Section 8.1.2 since we are installing non-residential 
sprinklers. Would a single sprinkler be required to protect both the gas grill 
and fireplace in this outdoor living area since they are considered fuel-fired 
equipment, or would separate sprinklers be required for the gas grill and 
fireplace? Also, would the 0.05 gpm/ft density apply to the outdoor living 
space or would the 0.1 gpm/ft density apply? In response to your question, we 
have reviewed NFPA 13D, 2013 edition as the applicable standard. Our informal 
interpretation is sprinkler protection is not required for open attached 
porches in one- and two-family dwellings.

 

Section 1.2.1 contains the purpose of NFPA 13D, which states:

 

The purpose of this standard shall be to provide a sprinkler system that aids 
in the detection and control of residential fires and thus provides improved 
protection against injury and life loss.

 

Then the NFPA 13D and R Handbook, Automatic Sprinkler Systems for Residential 
Occupancies Handbook commentary clarifies this by stating “the standard’s focus 
is life safety at a reduced overall system cost and therefore does not require 
sprinkler protection in all areas of the home. In line with this philosophy, 
the standard also only requires two operating sprinklers discharging for a 
period of 10 minutes to control the fire — a time period considered sufficient 
for occupant evacuation. At the end of this time period, if the fire has not 
been extinguished it will continue to burn and cause greater property damage. 
As a result, the standard does not specifically address property protection as 
its purpose." The purpose of NFPA 13D needs to be kept in mind when determining 
the sprinkler installation requirements for one- and two-family dwellings.

 

Since the purpose is to focus on life safety at a reduced overall system cost 
Section 8.3.4 states:

 

Sprinklers shall not be required in garages, open attached porches, carports, 
and similar structures.

 

Thus, sprinklers are not required for open attached porches, regardless of the 
contents on the porch. Section 8.3.5.1.2 does not apply to this situation 
because Section 8.3.5.1.2 only applies to the locations listed in Section 8.3.5 
since it is underneath Section 8.3.5. Section 8.3.5 states:

 

Sprinklers shall not be required in attics with or without storage, penthouse 
equipment rooms, elevator machine rooms, concealed spaces dedicated exclusively 
to and containing only dwelling unit ventilation equipment, floor/ceiling 
spaces, elevator shafts, crawl spaces, and other concealed spaces that are not 
used or intended for living purposes.

 

Section 8.3.5.1.2 can only be applied to the listed locations. The NFPA 13D and 
R Handbook commentary for Section 8.3.5.1.2 only refers to fuel-fire equipment 
in the locations listed in Section 8.3.5, further illustrating Section 
8.3.5.1.2 can only be applied in the locations listed in Section 8.3.5.