sprinklernotes
Water Delivery Times for Dry-systems

 

 

You asked the following questions: “In performing the timed water delivery test 
for dry systems, are you required to have a constant and steady stream of water 
discharging through the inspectors test connection to pass the test?” In 
response to your question, we have reviewed NFPA 13, 2016 edition as the 
applicable standard. Our informal interpretation is water is just needed to 
initially discharge from the test connection outlet.

 

It is nearly impossible to meet a water delivery time requirement for dry pipe 
sprinkler systems if you have to discharge a constant stream of water to the 
test connection and purge all of the air from the system in a timely manner. 
The annex section of A.25.2.3.2.3 tells us the test criteria is based on the 
first evidence of waterflow to the inspector’s test and air can be mixed with 
water for several minutes until the air is completely purged from the system. 
Additionally, in the 2016 NFPA 13 Handbook there is a FAQ on page 1091 
discussing this very topic titled, what is meant by “first evidence of 
waterflow” and the answer is as follows. “The measurement of the time for water 
to be discharged from the inspector’s test connection is based on the first 
evidence of waterflow, because it would be subject to interpretation if waiting 
was required to determine when a steady flow rate was achieved. During testing, 
the water discharging from the inspector’s test connection will initially be 
erratic, with spurting and momentary stoppages, due to mixing with air that is 
still in the system.” One thing to keep in mind, if it were a real fire event 
and more than one sprinkler activated the air would be purged from the system 
at a faster rate that it would from just a single outlet.    