sprinklernotes

Vertical Obstructions 18 inches or Less Below the Sprinkler Deflector

You asked the following question: “We have a system being designed as an 
ordinary hazard group 2. There are walls that do not go all the way to the 
ceiling. In some places, we have a clearance of 18 in. or more between the top 
of the wall and the deflectors, but in others, it is less than 18 in. For the 
latter, section 8.6.5.2.2.1 allows less clearance but only for light hazard 
occupancies. How should I address these partial walls?” In response to your 
question, we have reviewed NFPA 13, 2016 edition as the applicable standard. 
Our informal interpretation is below.

This is really a two-part question. Let’s first talk about walls that stop more 
than 18 inches below the plane of the deflector. Walls are ignored when the top 
of it is more than 18 inches below the plane of the deflector. It is 
understandable that most AHJ’s would be concerned about the shadow created by 
the partial wall. As crazy as it may sound, we ignore these items. When 
reviewing this issue, it helps if one keeps in mind that the primary function 
of the sprinkler is to control the upper layer temperature so as to avoid 
flashover. The only driving requirement is in section 8.5.6.1 that states: 
“unless the requirements of 8.5.6.2, 8.5.6.3, 8.5.6.4, or 8.5.6.5 are met, the 
clearance between the deflector and the top of storage or contents of the room 
shall be 18 in. (450 mm) or greater.” The partial wall should be viewed the 
same as a bookshelf that is full but doesn’t go all the way to the ceiling. 
Just like a bookshelf, the wall is not a structural member and acts simply as 
something contained within the space. As such, it would need to be 18 in. or 
more below the deflector.

As you identified, there is criteria for floor-mounted vertical obstructions 
(such as walls that don’t go to the ceiling) in section

8.6.5.2.2. This section is an allowance whereby the contents of the room can 
violate the 18-in. clearance required by section

8.5.6.1. It is limited to lower hazard fires as posed by light hazard 
occupancies. As shown in Table 8.6.5.2.2, allowed obstructions start at 3 in. 
below the deflector and stops at 18-in. below the deflector. Once you hit 18 
in. from the deflector, there’s no required minimum separation distance per 
this section. Once past 18-in., there’s no minimum required separation for any 
applications when using spray sprinklers (other sprinklers such as CMSA and 
ESFR have a minimum clearance of 36 in.). This also supports the understanding 
that we ignore partial walls that are greater than 18-in. below the deflector.

So, what do you do in an ordinary hazard occupancy when you don’t have an 
18-inch clearance? One choice is to install an additional sprinkler (as 
discussed in section 8.6.5.1.1) on the other side of the partial wall. Another 
option is presented by section 8.6.5.2.1.7 that states: Sprinklers shall be 
permitted to be installed on the centerline of a truss or bar joist or directly 
above a beam, provided that the truss chord or beam dimension is not more than 
8 in. (200 mm) and the sprinkler deflector is located at least 6 in. (150 mm) 
above the structural member and where the sprinkler is positioned at a distance 
three times greater than the maximum dimension of the web members away from the 
web members. From the sprinkler’s perspective, the top of a beam and the top of 
a partial wall looks the same (aka has the same impact on the discharge 
pattern). As such, it is entirely appropriate to apply this allowance to 
partial walls that meet the same defined dimensions. Since this is not 
explicitly identified by NFPA 13, the AHJ would have to concur and as I always 
say, discussing such things BEFORE the submittal is the best approach.

Reply via email to