sprinklernotes
Sprinkler Protection Requirements for Non-Combustible Exterior Canopies Used 
for Outside Dining

 

 

You asked the following questions: “We have a restaurant with a non-combustible 
canopy on the outside of the building with tables under the canopy with access 
from the building. The fire marshal is requiring sprinklers per the 2015 IBC 
sections 903.2.1, 903.2.1.2, and 903.2.1.7. Are sprinklers required?” In 
response to your question, we have reviewed NFPA 13, 2013 edition as the 
applicable standard. Our informal interpretation is that sprinklers will not be 
required.

 

The AHJ is correct that the fire area or the building must be protected with a 
fire sprinkler system per section 903.2.1. Additionally, the building code 
tells us WHEN to protect the area or the building per the applicable NFPA 
standard, in this case, NFPA 13. NFPA 13 allows the omission of sprinklers in 
certain areas such as exterior canopies when specific conditions are met. The 
IBC still classifies buildings with areas where protection is omitted by NFPA 
13 as fully protected. The patio cover is constructed of noncombustible 
construction. It is used only for dining purposes and will contain only tables 
and chairs. There are no heat sources such as barbeque grills. NFPA Subsection 
8.15.7.2 allows for the omission of sprinklers below canopies if they are 
constructed of limited or non-combustible materials.

 

There is one section that can negate omitting protection. Section 8.15.7.5 will 
require sprinklers under non-combustible canopies that are more than 2-ft wide 
if combustible materials are being stored under them. Patio-type furniture will 
not necessitate the installation of sprinklers. This is addressed in the 2013 
edition of NFPA's Automatic Sprinkler Systems Handbook under section 8.15.7.5. 
It states that the committee has stated that combustibles, such as patio 
furniture, which may be wood or plastic and including cushions, are not 
sufficient to justify sprinkler protection. So, if no heat sources such as 
barbeque grills or heaters are allowed under the patio cover, sprinklers should 
not be required. When heat sources are present, then sprinklers are required. 
The commentary states, However, judgment is needed, and sprinklers may be 
justified where the balcony contains combustible loading, such as patio 
furniture, AND where barbeque grills are allowed or other ignition sources are 
present, such as a furnace located off of, and accessed from, the balcony. 
Thus, if heaters are present with the patio furniture, sprinklers will be 
required. Such an arrangement is not considered a significant risk for two 
reasons. One is the fact that individual or isolated sets of tables and chairs 
are difficult to ignite, thus the restriction of heat sources. The second is 
that such rooms that are completely open to the exterior are extremely unlikely 
to reach flashover. Now if the tables and chairs are stacked for storage during 
the off-season, that presents a significantly different fuel package and 
sprinkler protection would be required. In conclusion, sprinkler protection is 
not required beneath the exterior projection.