sprinklernotes
Intermediate Temperature Sprinklers Installed Throughout a Light Hazard 
Occupancy.

 

 

You asked the following questions: “We have a customer who had Joint Commission 
inspection this week at his hospital. One of the inspectors has questioned us 
installing intermediate temperature QR sprinklers throughout a light hazard 
occupancy. I tried to explain that in 2010 the code was revised to allow for 
ordinary and intermediate temp QR sprinklers to be installed throughout the 
building. Unfortunately, the inspectors do not interpret section 8.3.2.1 like 
that. Are intermediate temperature sprinklers allowed to be installed 
throughout light hazard occupancies?” In response to your question, we have 
reviewed NFPA 13, 2010 edition as the applicable standard. Our informal 
interpretation is that intermediate temperature sprinklers can be installed 
throughout the premises.

 

Historically, the base requirement per 8.3.2.1 was to use an ordinary 
temperature rating throughout all buildings unless higher localized 
temperatures required a higher rating. There was also the allowance to go to a 
high temperature rating for extra hazard occupancies and storage. This was 
changed in the 2010 edition whereby one could also install sprinklers with an 
intermediate temperature rating throughout all facilities. This section says 
unless the requirements of 8.3.2.2, 8.3.2.3, 8.3.2.4, or 8.3.2.5 are met, 
ordinary- and intermediate-temperature sprinklers shall be used throughout 
buildings. The substantiation for this change in the 2009 Report on Proposals 
in 13-125 Log #89 stated, Many commercial facilities are omitting a drop 
ceiling (simply painting the upper area black) and often installing many HVAC 
diffusers. This has led to some cases where 1/3 of the sprinklers have an 
intermediate rating in order to satisfy Table 8.3.2.5(a). With standard 
response sprinklers a lower temperature rating makes sense. Now that 
quick-response sprinklers are required, the difference in activation time 
between the two temperature ratings is not significant but the impact on 
installation is significant. The handbook commentary for this section says that 
traditionally, ordinary-temperature sprinklers have been required throughout a 
building unless the requirements of 8.3.2 required intermediate- or 
high-temperature sprinklers to be used. However, many buildings are built 
without suspended ceilings, resulting in a mix of ordinary with the 
intermediate-temperature-rated sprinklers needed around heating diffusers and 
other heat-producing areas. Since the response time of quick-response 
intermediate-temperature sprinklers are not that different from 
ordinary-temperature standard-response sprinklers, the standard now groups 
ordinary- and intermediate-temperature sprinklers together and allows 
intermediate-temperature sprinklers throughout the building, reducing the need 
for multiple types of sprinklers. Section 8.3.2.4 applies where sprinklers are 
installed in specific locations as required by 8.3.2.5.