sprinklernotes
Galvanized Piping Requirements for Dry and Preaction Sprinkler Systems

 

 

You asked the following questions: “We have an attic protected by a dry system 
using Viking Attic Sprinklers. Will this system be required to be galvanized 
per 8.4.7.2.1?” In response to your question, we have reviewed NFPA 13, 2010 
edition as the applicable standard. Our informal interpretation is that 
internally galvanized steel piping is not required on dry pipe and preaction 
systems using other than CMSA sprinklers and other situations noted below.

 

Section 8.4.7 of NFPA 13 addresses special requirements for CMSA sprinklers. 
Sections 8.4.7.1 and 8.4.7.2.1 are subsections of 8.4.7 and set requirements 
that only apply to the use of CMSA sprinklers and do not apply to any other 
sprinkler types. Thus, NFPA 13 does not require galvanized pipe for all dry 
pipe and preaction systems. There is some misconception that all dry pipe and 
preaction systems are required to have galvanized piping. Dry pipe and 
preaction systems can be black steel except for a few applications. The dry 
pipe and preaction system piping must be corrosion resistant or internally 
galvanized when small orifice K-factor 4.2 sprinklers protect light hazard 
occupancies according to Section 8.3.4.3. Water-cooling towers under the 
Special Occupancy Requirements Chapter in Section 21.21.2.10.1 require the 
piping, fittings, hangers, braces, and attachment hardware including fasteners 
shall be hot-dip galvanized steel or use other materials that have a superior 
corrosion resistance. Two other sections that require galvanized pipe are 
Section 6.9.3.3 that requires all piping to water motor-operated devices shall 
be galvanized or brass or other corrosion-resistant material acceptable under 
this standard, and Section 6.9.3.4 that piping between the sprinkler system and 
a pressure-actuated alarm-initiating device shall be galvanized or of 
nonferrous metal or other approved corrosion-resistant material. Thus, there is 
no carte blanche requirement that all dry pipe and preaction systems must have 
galvanized piping.