sprinklernotes
ESFR Sprinklers and Obstructed Combustible Construction

 

 

Previously before the 2019 edition of NFPA 13, ESFR sprinklers were not 
permitted to be installed in combustible obstruction per section 8.4.6.3. For 
the 2019 Edition Section, 8.4.6.3 was moved to section 14.2.4 and revised to 
say ESFR sprinklers shall be permitted for use in buildings with unobstructed 
or obstructed construction. Additionally, a subsection of 14.2.4.1 was added 
that states: Where depths of the solid structural members (beams, stem, and so 
forth) exceed 12 in. (300 mm), ESFR sprinklers shall be installed in each 
channel formed by the solid structural members. Unfortunately, the technical 
committee didn’t update Table 14.2.8.2.1 to reflect that ESFR sprinklers are 
now allowed in combustible obstructed construction which created a conflict 
within the standard. The Tech Services department at the AFSA noticed the 
conflict during a review of the changes and submitted a TIA 19-4 for table 
14.2.8.2.1 to be modified and resolve the conflict the committee created. On 
August 5-7, 2019, during the standards council meeting, they voted to approve 
TIA # 19-4. The document can be found here 
<https://www.nfpa.org/assets/files/AboutTheCodes/13/TIA_13_19_4.pdf>. 