sprinklernotes
Sprinkler Temperature Ratings for Attics.

 

 

You asked the following questions: “I have a two-story assisted living facility 
with a sprinklered attic. What temperature classification for the sprinklers is 
required in the attic?” In response to your question, we have reviewed NFPA 13, 
2016 edition as the applicable standard. Our informal interpretation is 
intermediate temperature rated sprinklers shall be used.

 

There are two sections in NFPA 13 that address sprinkler temperature rating 
requirements with regard to the conditioning of the environment in which they 
are installed. In your case, we are discussing an attic. Section 8.3.2.5 
addresses the issue by giving you eight common situations. Number 5 tells us 
the sprinklers in an unventilated attic require intermediate temperature 
classification. Now, there is also table 8.3.25(b) which indicates that 
intermediate temperature rated sprinklers are to be used in both ventilated and 
unventilated attics. So, in applying these two provisions - intermediate 
temperature rated sprinklers should be installed unless the maximum ambient 
temperature in the space exceeds 150 degrees F per Table 6.2.5.1 in which case 
high temperature rated sprinklers are required. 