sprinklernotes
Slatted Ceilings and Sprinkler Protection

 

 

You asked the following questions: “We have a building that has wood veneer 
slat ceiling features. The slats are 5/8-in. wide and 3-1/4 in. deep with a 
1-3/8 in. gap between the slats. The area above the slatted ceiling is 
constructed of noncombustible steel joist framing and roofing. Are sprinklers 
required above the slatted area?” In response to your question, we have 
reviewed NFPA 13, 2016 edition as the applicable standard. Our informal 
interpretation is that sprinklers below the wood-slatted ceilings are not 
required.

 

Sprinklers located below the decorative wood would be essentially ineffective 
unless the sprinkler is located directly in the fire plume. There is no ceiling 
to collect heat to activate sprinklers. Fire sprinklers opening above them at 
the floor or roof deck would cold solder the sprinklers located below. This 
application also does not appear to be a traditional grid ceiling. The NFPA 13 
standard considers an open grid ceiling when the openings are ¼ in. or larger 
in the least dimension, where the thickness or depth of the material does not 
exceed the least dimension of the opening, and where such openings constitute 
70 percent of the area of the ceiling material. The sprinkler discharge pattern 
can be affected by the open grid ceiling, so sprinkler spacing requirements are 
provided in section 8.15.14. The decorative wood is suspended with the longer 
leg vertical from the floor or roof deck above where the obstruction rules 
should be applied. If you use standard spray sprinklers and if the decorative 
wood is located more than 18 inches below the deflector, the wood obstruction 
can be ignored according to section 8.6.5.3.1. This applies to obstructions 
greater than 18 inches below the deflector, and sprinklers shall be installed 
under fixed obstructions over 4 ft wide. If the decorative wood falls within 18 
inches of the deflector where water can spray above and below an obstruction or 
can spray on both sides of an obstruction such as a column, then section 
8.6.5.2.1.3 applies. This is commonly known as the three-times rule. This 
section indicates that sprinklers shall be positioned away from obstructions a 
minimum distance of three times the maximum dimension of the obstruction (e.g., 
structural members, pipe, columns, fixtures). Thus, this could be a tedious 
process to verify each wood slat member is located according to this rule. The 
ceiling could be considered grouped obstructions, but NFPA 13 does not provide 
specific guidance. The committee did address a comment for grouped obstructions 
during the 2009 Report on Comments in 13-119 Log #234 with an action of Reject. 
The submitter proposed a new section 8.5.5.3.3.4 that stated, Grouped 
Obstructions. Closely spaced obstructions shall be considered a single 
obstruction when the space between individual obstructions is smaller than the 
width of the smaller adjacent obstruction. A.8.5.5.3.3.4 When there are more 
than two adjacent obstructions, the width of the grouped obstruction is 
intended to include any additional obstructions that do not meet the separation 
requirement. The committee rejected this proposal since insufficient material 
to inform a Committee Action on this item. This leaves us with the existing 
obstruction rules in NFPA 13. With that said, standard spray sprinklers are 
fairly tolerant of obstructions. The sprinklers have the ability to get water 
on both sides of the obstruction without allowing a significant dry shadow on 
the other side of the obstruction. This works for continuous and isolated 
obstructions where the sprinkler can throw water over and under the 
obstruction. This keeps the upper layer gases in the room cool, thus preventing 
flashover and controlling the fire. Additional factors to consider are the 
building construction and occupancy classification of the space: 1.The ceiling 
or roof deck is of noncombustible construction, and that is very tolerant of 
fire exposure. 2.The area where the wood-slatted ceilings are placed is a lobby 
and or a corridor (light hazard occupancy). 3.The quantity and/or 
combustibility of contents are low, and fires with relatively low rates of heat 
release are expected.