Disconnects for Electric Fire Pump Controllers

 

 

You asked the following questions: “If installing a disconnect and external 
overcurrent protection devices for an electric fire pump controllers, first is 
it allowed and second can they be located inside the fire pump room?” In 
response to your question, we have reviewed NFPA 20, 2016 edition as the 
applicable standard. Our informal interpretation is that overcurrent protection 
is allowed to be installed and, if necessary, can be installed inside the pump 
room.

 

Section 9.2.3 allows one disconnecting means and associated overcurrent 
protection device of electric service to the fire pump provided your power 
supply arrangement complies with Section 9.2.2 and Subsections 1, 2, 3, or 5. 
The Handbook commentary for Section 9.2.3 states the single upstream disconnect 
permitted by Section 9.2.3 affords disconnection for activities such as 
maintenance and is not intended to be operated under fire conditions. 
Additional disconnecting means would reduce the reliability of the fire pump, 
since these disconnects can be remote from the fire pump room, typically not 
easily located makes it difficult to manage especially during a fire event.  
The intent behind these sections is to make sure the pump will run regardless 
of any problems during a fire scenario until the pump destroys itself. Fire 
pumps themselves are sacrificial and are typically only allowed to be stopped 
to preserve the integrity of the system piping. That said, the approved 
location of the disconnect will need to be tapped in ahead of the main service 
building, to avoid any advertent interruption to the fire pump, due to any 
power shutdown to the building.

 

Now regarding the location of the disconnecting means and associated 
overcurrent device. The NFPA 20 handbook commentary for Section 9.2.3.1 (3) 
gives a few examples of acceptable locations. A fire pump disconnect is 
considered to be remote from disconnects for other non-fire pump loads when it 
is not within sight of the other disconnects. Means of achieving this include 
locating the fire pump disconnect in a different room from where the other 
disconnects are located, or if in the same room, the disconnects are separated 
by building construction or permanently installed equipment that provides 
separation, such that all disconnects are not within sight from any location 
within the room.

 

In closing, if you meet the requirements of Section 9.2.2 and Section 9.2.3 you 
can use an overcurrent protection device, and it can be located within the same 
room provided they are separated by building construction or permanently 
installed equipment that provides separation, such that all disconnects are not 
within sight from any location within the room.