You asked the following questions: “We are installing a sprinkler system in a 
residence per NFPA 13D. We have a closet under the stairs that is less than 400 
cubic feet in size. The AHJ is requiring a sprinkler to be located at the low 
point in the closet, which is under the intermediate landing of the stairs. His 
justification was that the stairs are a means of egress in a fire event. Is a 
sprinkler required at the low point of the closet?” In response to your 
question, we have reviewed NFPA 13D, 2016 edition as the applicable standard. 
Our informal interpretation is that with a closet not larger 400 cu. ft. size, 
a single sprinkler at the highest ceiling elevation shall be sufficient without 
regard to obstructions or minimum distance to the wall.

 

The small areas in closets under the intermediate landing of stairs are usually 
filled with storage and will prevent the activation of the sprinkler in a fire 
event. With that being said, this section does mention minimum distances and 
does not mention maximum distances. The minimum distance is a problem since the 
sprinkler has to be kept out of the 4-in dead air space pocket created where 
the wall, ducts, or equipment intersects the ceiling. The maximum distance was 
not mentioned since this is not a concern for such a small space. This is 
supported by the commentary in the Sprinkler Systems for Residential 
Occupancies Handbook. This commentary indicates that in a small closet, the 
possibility of heat from a fire setting off a sprinkler is not a concern, 
regardless of where that sprinkler is in relation to the other objects that 
might be near the ceiling. The possibility of water spray absorbing the heat 
and helping to control the fire is also not an issue since the whole space will 
be flooded with water. Water will be bouncing off the walls and getting to the 
fire from many directions. A closet with 400 cu. ft. in volume will typically 
be about 50 sq. ft. in area, assuming an 8- ft high ceiling. At a minimum 
pressure of 7 psi, a sprinkler with a K-factor of 4.1 will discharge 10.8 gpm, 
creating a density of 0.22 gpm/sq. ft. in the closet, which is more than four 
times the density required for residential sprinklers. This excess density in a 
small space will more than make up for the obstructions caused by light 
fixtures or other items near the sprinkler. There is additional information in 
Supplement 2 of the Sprinkler Systems for Residential Occupancies Handbook that 
says the same thing. It also indicates that with a ceiling height of 8 ft to 10 
ft, this would have a floor area of approximately 40 sq. ft. to 50 sq. ft. 
While this size room was never tested in full-scale fire tests, the committee 
was sure that this did not represent a significant problem as long as the 
sprinkler would open. Lastly, there is not a concern of getting water to the 
farthest distance under the stairs or getting the entire floor area wet. While 
this annex material is not referenced in NFPA 13D it does give us some guidance 
and the same issue is directly addressed in the 2016 edition of NFPA 13R in 
annex material A.6.4.6.3.2, that indicates in such small closets, a single 
sprinkler installed at the highest point will help contain a fire by cooling 
the hot gases that will collect at the uppermost point. There can be many 
different obstructions that will prevent water from reaching all portions of 
the closet or compartment. The annex gives three common examples: (1) Heating 
and air conditioning closets where the plenum totally blocks the spray pattern 
and in some cases only 4 inches or less exists between the wall and the plenum 
for the sprinkler; (2) Globe or fluorescent lights in closets that hang down 
obstructing the sprinkler; and (3) Closets under stairs that switchback where 
the spray pattern will not reach the low side. Number 3 acknowledges water will 
not reach the far spaces under the stairs where sprinklers do not have to spray 
to the lower portion of the closet area.