Mixing of Sprinklers with Different Temperature Ratings in The Same Compartment

 

 

You asked the following questions: “I have an AHJ questioning the placement of 
a 165-degree concealed pendent in the same area as a 155-degree recessed 
pendent.  I have tried to explain to him that they are both of ordinary 
temperature rating, but he is concerned about skipping.” In response to your 
question, we have reviewed NFPA 13, 2016 edition as the applicable standard. 
Our informal interpretation is a 165-degree sprinkler can be installed in the 
same compartment as a 155-degree sprinkler.

First, 165-degree sprinklers and 155-degree sprinklers are both rated as 
ordinary temperature per Table 6.2.5.1. NFPA 13, Chapter 8 provides multiple 
scenarios where high temperature rated sprinklers are required to be installed 
within the same compartment as ordinary temperature rated sprinklers, including 
near heat-producing sources. 

 

While NFPA 13 does provide a restriction on mixing sprinklers with different 
response-time indexes (RTI) (ie: standard response and quick response) there is 
no restriction on mixing sprinklers of mixed temperature ratings within a 
system or within a compartment.

 

I would also note there is also no restriction on mixing sprinklers with 
differing orientations within a compartments (ie., upright, pendent, and/or 
sidewall sprinklers) or even standard spray adjacent to extended coverage, 
provided they are all of the same RTI. 

Reply via email to