sprinklernotes
Antifreeze Systems with Backflow Preventers

 

 

You asked the following question: “We have an NFPA 13 system that will be using 
listed antifreeze for the entire structure.  After the backflow preventer 
(BFP), the riser assembly will be the typical vertical orientation.  Does 
Figure 7.6.3.3 require the components after the BFP to be in a horizontal 
orientation?”  In response to your question, we have reviewed NFPA 13, 2016 
edition as the applicable standard.  Our informal interpretation is the riser 
is not required to be horizontal.

 

A primary function of Figure 7.6.3.3 is simple to show that the standard drop 
loop required when using a check valve (with a 1/32-in hole) is not necessary 
when the assembly includes a backflow preventer.  The drop loop was to minimize 
the migration of the antifreeze solution when pressure was relieved (due to 
thermal expansion) through the hole in the check valve.  When a BFP is used 
there is no migration and pressure is relieved by the use of an expansion 
chamber.  As such, a drop loop is not needed.  Although the orientation of the 
assembly is irrelevant, some of the components must be located as indicated in 
relation to the sprinklers.  As common sense would dictate, the drain valve 
must be located at a low point and the fill cup must be above the plane of the 
sprinklers.  Naturally, if a fill connection (pressure-driven) is used instead 
of a fill cup, then its placement in reference to the sprinklers is irrelevant.

Reply via email to