Residential Sidewalls and Soffits

 

 

You asked the following questions: “Section 8.7.4.1.3.3 of NFPA 13, 2016 
edition allows standard sidewall sprinklers to be installed under a soffit when 
both the minimum distance from the sprinkler deflector to the bottom of the 
soffit and maximum distance from the sprinkler deflector to the high ceiling is 
maintained.  There is no applicable section or provision in NFPA 13, 2016 
edition for residential sidewall sprinklers.  Are residential sidewall 
sprinklers permitted to be installed under a soffit if both the minimum 
distance from the sprinkler deflector to the bottom of the soffit and maximum 
distance from the sprinkler deflector to the high ceiling is maintained?” We 
have reviewed NFPA 13, 2016 edition that you indicated as the applicable 
standard. Our informal interpretation is that the soffit requirement for 
sidewall spray sprinklers should also apply to residential sprinklers.

 

Although the allowance for a sidewall sprinkler to be installed beneath a 
soffit is identified only in section 8.7, this does not mean that the 
underlying reasons for its allowance applies only to spray sprinklers.  This 
just means that the public input was submitted on section 8.7 and the committee 
did not consider its broader application.  This is a common consequence of 
having to process such a large number of public inputs.  The basic evaluation 
for this issue as identified in section 8.1.1(3) is whether there is 
satisfactory performance with respect to activation time and distribution.  
Considering that the thermal link is the same for both sprinklers, the 
activation will effectively be the same.  The committee obviously considered 
the impact on activation time to be negligible.  Considering that the soffit is 
not in the path of the water discharge, the performance regarding discharge is 
unaffected.  As such, there is no logical reason not to extend the same 
criteria to residential sidewall sprinklers.  Since this is not explicitly 
identified in NFPA 13, concurrence by the AHJ is required.