sprinklernotes
Sprinklers on Entryways in NFPA 13R

 

 

You asked the following questions: “Front entryways have been determined by a 
local inspector to require sprinklers per code.  Are sprinklers required on 
entryway patios?” In response to your question we have reviewed NFPA 13R, 2016 
edition that you indicated as the applicable standard as well as the 2016 
edition and the 2018 editions of the International Building Code (IBC) and the 
International Fire Code (IFC). Our informal interpretation is that sprinklers 
for entryways are not required.

 

The likely confusion seems to stem from the IBC and the IFC requirement for 
balconies to be protected in which the state or local code is based. The 
commentary from this section says balconies, decks, and patios in buildings of 
Type V construction and used for Group R occupancies are required to have 
sprinkler protection when there is a roof or deck above. This is in addition to 
the requirements of NFPA 13R, which primarily addresses the life safety of 
occupants and not property protection. The intent is to address hazards such as 
grilling and similar activities. Entryways to dwelling units are not usually 
exposed to grilling or similar activities. Section 6.6.5 is explicit in NFPA 
13R where it states, “Sprinklers shall not be required in any porches, 
balconies, corridors, carports, porte cocheres, and stairs that are open and 
attached.” The annex for this section says an example of an open corridor or 
breezeway is one that is exposed to the outside atmosphere (temperature) and 
empties to an unenclosed stairway and has no doors attached to it. Another 
example is an exterior wraparound corridor that is typical in a two- to 
three-story motel. The 2016 handbook commentary says mandatory sprinkler 
protection for many of the areas in section 6.6.5 and section 6.6.6 would 
necessitate the use of dry pipe or antifreeze systems in areas where freezing 
weather is encountered. Such systems would dramatically impact the cost of the 
sprinkler systems without correspondingly increasing the life safety offered by 
the sprinkler system. Very few deadly fires tend to start in these spaces. This 
concept should extend to all outdoor portions of the building including 
drive-up areas, breezeways, and porte-cocheres even though they are not 
mentioned by name in NFPA 13R.

 

Sprinkler protection should not be required for these spaces outside of the 
building. However, it should be noted that where the spaces described in 
section 6.6.6 contain fuel-fired equipment, sprinklers are required. Based on 
the statistics provided in Table A.1.2, the limited number of fatalities caused 
by fires that start in these areas does not warrant the sprinkler protection 
being required in these spaces. Owners can require that their design 
professionals incorporate sprinklers into these areas, if so desired. Note that 
section 6.6.5.1 was added to the 2013 edition of NFPA 13R and is aligned with 
the building code requirement by providing new text. It states where a roof or 
deck is provided above, sprinklers shall be installed to protect attached 
exterior balconies, attached exterior decks, and ground-floor patios serving 
dwelling units in buildings of Construction Type V. The handbook commentary 
under this section says that the committee has made a major shift regarding 
porches, balconies, decks, and ground floor patios serving dwelling units in 
buildings of Type V construction. Type V construction applies to the entire 
building, and not just the construction of the balcony. This rule applies to 
the exterior or open spaces accessible only from the dwelling unit itself, and 
not a corridor or breezeway that is shared among multiple dwelling units. The 
previous sentence provides a key statement regarding your question. As such, 
sprinklers are not required in the entryways.

Reply via email to