sprinklernotes

Window Sprinkler Within A Dwelling Unit

“We have designed and installed an NFPA 13R sprinkler system in a three-story 
apartment building. The system has been installed, and it has come to our 
attention that the architect designed a firewall that cannot have openings 
within 4 ft of the firewall and there are windows within 4 ft of the firewall. 
The local building code allows the use of a water curtain per NFPA 13 in front 
of the windows with this application. This application will have quick-response 
sprinklers installed in the compartment of a dwelling unit with residential 
sprinklers. Does this meet the NFPA 13 and 13R standards by installing 
quick-response sprinklers (for the water curtain) in the same dwelling unit 
compartment as the residential sprinklers?”

We have reviewed the 2019 editions of NFPA 13, Standard for the Installation of 
Sprinkler Systems, and NFPA 13R, Standard for the Installation of Sprinkler 
Systems in Low-Rise Residential Occupancies, that you indicated as the 
applicable standards. Our informal interpretation is that residential and 
quick-response window sprinklers can be within the same compartment.

There is no residential type window sprinkler; thus, a special quick-response 
window sprinkler has to be used. The issue is the thermal element where the 
compartment has to be either residential or quick-response sprinklers. The 
residential sprinkler and the quick-response window sprinkler are both 
fast-response type sprinklers so that shouldn’t be an issue for this 
application. Section 1.6 of NFPA 13R for new technology addresses this in 
section 1.6.1 which states that nothing in this standard shall be intended to 
restrict new technologies or alternate arrangements, provided the level of 
safety prescribed by this standard is not lowered. The materials or devices not 
specifically designated by this standard shall be utilized in complete accord 
with all conditions, requirements, and limitations of their listings per 
section 1.6.2. Section 5.1.1.4.2 of NFPA 13R also addresses special sprinklers. 
Special sprinklers shall be permitted to be listed for protection of a specific 
construction feature in a portion of an occupancy classification. Some other 
practical reasons this could be allowed is that the window sprinkler would 
likely be located at a lower elevation than the ceiling or sidewall sprinklers. 
In addition, the window sprinkler may be located behind a curtain, window 
shade, or blinds. A fire exposing on the window would likely activate the 
window sprinkler first before the room sprinklers would activate. If the room 
sprinklers did activate first, the effects of that are not expected to be 
adverse. There are larger issues occurring on the outside of the window. An 
incorrect application of these two sprinkler types would be using the window 
sprinkler to cover part of the dwelling unit in lieu of residential sprinklers. 
That is not the case for this application. NFPA 13 in section 12.1.4 does 
address residential sprinklers installed in a compartment as defined in section 
3.3.38 that all sprinklers within the compartment shall be residential 
sprinklers. The Automatic Sprinkler Systems handbook commentary indicates that 
when mixing sprinklers that are not of the same make, caution is needed to 
avoid the possibility of reverse operating order or spot operation of 
sprinklers. It is important that all residential sprinklers be of similar 
thermal sensitivity when they are installed in a compartment. The use of 
bulb-type and solder-type sprinklers or residential and other types of 
sprinklers is acceptable, as long as all of the sprinklers in the compartment 
are fast-response sprinklers as defined in section 3.3.205.2(1)(a). Section 
12.1.4 changed from fastresponse type in the 2010 edition to residential 
sprinklers in the 2013 edition. However, the commentary has remained unchanged 
since the 2010 edition until the 2019 edition, where it was deleted from the 
handbook during the