“I am trying to apply figure A.10.2.7.1.2 to a bulkhead with a demising wall 
above it stepped back about 8 in. from the front edge of the bulkhead. Below 
the bulkhead is a floor to bulkhead wall that is stepped back 2 ft-8 in. from 
the front edge of the bulkhead. Two feet of the depth below the bulkhead is 
filled with a full height built-in cabinet. The AHJ is not comfortable allowing 
this code to be applied in my situation because the wall is not in the same 
vertical plane above and below the bulkhead. I do not see any dimensions in 
figure A.10.2.7.1.2 that give a depth of the setback for the wall. The figure 
only gives a maximum depth of 4 ft. I am well under this total width and my 
sprinkler head is 20 in. above the top of the bulkhead. Can I apply this code 
to avoid installing a sprinkler in the 8-in. wide bulkhead in front of the 
cabinet?”

We have reviewed NFPA 13, Standard for the Installation of Sprinkler Systems, 
2019 edition that you indicated as the applicable standard. Our informal 
interpretation is that a sprinkler is not required in the 8-in. bulkhead.

A cabinet fills the void where an 8-in. shelf against the wall is present. The 
standard does reference in section 9.5.3.2.2 that the distance from the wall to 
the sprinkler shall be measured to the wall behind furniture, such as 
wardrobes, cabinets, and trophy cases. That is to address the correct placement 
of the sprinkler. What the standard does not say is to omit this cabinet when 
considering obstructions. As such, the cabinet becomes the face of the wall 
when applying the obstruction rules. This should not be considered as a 2 ft-8 
in. niche. This application is an 8-in. shelf against the wall. Section 
10.2.7.1.1 indicates that sprinklers shall be located so as to minimize 
obstructions to discharge as defined in sections 10.2.7.2 and 10.2.7.3, or 
additional sprinklers shall be provided to ensure adequate coverage of the 
hazard. Since the obstruction is located 20 in. below the deflector, section 
10.2.7.3.1 would apply. More specifically, sprinklers shall be installed under 
fixed obstructions over 4-ft wide, such as ducts, decks, open grate flooring, 
cutting tables, and overhead doors per section 10.2.7.3.2. Hence, figure 
A.10.2.7.1.2 specifically shows your application. The vertical plane above and 
below the obstruction doesn’t appear to be of a concern for this application as 
both surfaces will be wetted. If, for instance, the distance from the deflector 
to the shelf was less than or equal to 18 in., section 10.2.7.2.1.2 would refer 
back to section 10.2.7.1.2. Applying section 10.2.7.1.2(3), nicknamed the 
soffit rule, this would place the sprinkler a minimum of 20 in. away from the 
obstruction to the centerline of the sprinkler. The sprinkler is located at 24 
in., thus you met the intent of the standard.