sprinklernotes

Sprinklers in Closets

The following information was provided: NFPA 13-2019 section 9.2.4.2 allows the 
omission of sprinklers in closets under 24 ft2. “Sprinklers are not required in 
clothes closets, linen closets, and pantries within dwelling units in hotels 
and motels where the area of the space does not exceed 24 ft2. and the walls 
and ceilings are surfaced with non-combustible or limited-combustible 
materials.”
 
You asked the following question: Are fire sprinklers required in closets less 
than
24 ft2 in a condominium hotel with and occupancy classification of R-2?
 
In response to your question, we have reviewed NFPA 13, Standard for the 
Installation of Sprinkler Systems, 2019 edition.

Our informal interpretation: The intent of section 9.2.4.2 is to omit 
sprinklers in small closets in hotels and motels due to their transient 
occupancy. Because the primary use of an R-2 occupancy could include 
semi-permanent residency with the possibility of long-term storage in the 
closets, sprinklers should be installed.
 
The 2018 IBC provides examples of R-2 occupancies in section 310.3 which 
includes the following:

        • Apartment houses
        • Congregate living facilities (nontransient) with more than 16 
occupants
        • Boarding Houses
        • Convents
        • Dormitories
        • Fraternities and sororities
        • Monasteries
        • Hotels (nontransient)
        • Live/work units
        • Motels (nontransient)
        • Vacation timeshare properties
 
The 2018 IBC specifically calls out that when the designation of hotels and 
motels are used for R-2 occupancies, the occupancy is nontransient. Because of 
this designation, sprinklers should be installed in the closets. AFSA intends 
to submit clarifying language for the 2025 edition to address this discrepancy.
 
Relief could be provided if NFPA 101 is applicable to the jurisdiction where 
this building is being constructed. Per NFPA 101-2018 for Lodging and Rooming 
Houses and New Apartment Buildings:
 
26.3.6.2.4 In buildings sprinklered in accordance with NFPA 13 closets less 
than 12 ft2 (1.1 m2) in area in individual dwelling units shall not be required 
to be sprinklered. 
 
30.3.5.3* In buildings sprinklered in accordance with NFPA 13, closets shall 
meet the following requirements:
(1)   Closets of less than 12 ft2 (1.1 m2) in individual dwelling units shall 
not be required to be sprinklered.
(2)   Closets that contain equipment such as washers, dryers, furnaces, or 
water heaters shall be sprinklered, regardless of size.