sprinklernotes

Sprinklers Under Combustible Drive-Through

The following information was provided: I have a drive-through that is over 
4-ft wide. It is constructed with steel beams wrapped on the sides and bottom 
with plywood with 2x12 wood joists 1 ft on center run on top on the beams, then 
a layer of plywood, then a waterproof membrane, then a metal roof deck. All of 
the exposed wood around the beams will be covered with a limited-combustible 
exterior insulation and finish system (EIFS). The EIFS will continue along the 
bottom of the 2x12s running from soffit to soffit with no insulation between 
the 2x12s above. The soffits around the steel beams will be filled with 
insulation or fire stopped to 160 ft3 per section 8.15.1.1. All exposed 
material is EIFS and metal roof. The AHJ has rejected our drawings and said 
unless the requirements of NFPA 13 section 8.15.7.1 are met, sprinklers shall 
be installed under this exterior drive-through. Also, unless the requirements 
of NFPA 13 section 8.15.1.2 and 8.15.7.3(1) are met for this drive-through for 
the unsprinklered combustible concealed spaces of this drive-through, these 
concealed spaces shall be fully sprinklered in accordance with NFPA 13 section 
8.15.1.1.
 
You asked the following question: In your opinion, does this drive-through 
require any sprinklers?
 
In response to your question, we have reviewed NFPA 13, Standard for the 
Installation of Sprinkler Systems, 2019 edition.

Our informal interpretation: Sprinkler protection can be omitted if the EIFS 
meets the definition of “limited-combustible” and if the combustible concealed 
space is compartmentalized or filled with noncombustible insulation as 
described above.
 
Per the pictures and the description, there are actually two components to this 
issue – a combustible concealed space and an exterior projection. The 
combustible concealed space is not required to be protected as stated by 
section 8.15.1.2.5.
 
8.15.2.3.5 Concealed spaces formed by ceilings attached directly to or within 6 
in.
(150 mm) of wood joist or similar solid member construction shall not require 
sprinkler protection.
 
It should be noted that omitting sprinklers in this scenario will require a 
minimum remote area of 3,000 ft2 for adjacent spaces.
 
For the exterior projection, the requirements of section 8.15.7 will determine 
the protection under the canopy.
 
8.15.7* Exterior Projections.
 
8.15.7.1 Unless the requirements of 8.15.7.2, 8.15.7.3, or 8.15.7.4 are met, 
sprinklers shall be installed under exterior projections exceeding 4 ft (1.2 m) 
in width.
 
8.15.7.2* Sprinklers shall be permitted to be omitted where the exterior 
canopies, roofs, porte-cocheres, balconies, decks, and similar projections are 
constructed with materials that are noncombustible, limited-combustible, or 
fire retardant– treated wood as defined in NFPA 703, or where the projections 
are constructed utilizing a noncombustible frame, limited-combustibles, or fire 
retardant–treated wood with an inherently flame-resistant fabric overlay as 
demonstrated by Test Method 2 in accordance with NFPA 701.
 
8.15.7.3 Sprinklers shall be permitted to be omitted from below the exterior 
projections of combustible construction, provided the exposed finish material 
on the exterior projections are noncombustible, limited-combustible, or fire 
retardant–treated wood as defined in NFPA 703, and the exterior projections 
contain only sprinklered concealed spaces or any of the following unsprinklered 
combustible concealed spaces:
 
(1) Combustible concealed spaces filled entirely with noncombustible insulation
 
(2) Light or ordinary hazard occupancies where noncombustible or 
limited-combustible ceilings are directly attached to the bottom of solid wood 
joists so as to create enclosed joist spaces 160 ft3 (4.5 m3) or less in 
volume, including space below insulation that is laid directly on top or within 
the ceiling joists in an otherwise sprinklered attic [see 11.2.3.1.4(4)(d)]
 
(3) Concealed spaces over isolated small exterior projections not exceeding 55 
ft2
(5.1 m2) in area
 
8.15.7.4 Sprinklers shall be permitted to be omitted from exterior exit 
corridors when the exterior walls of the corridor are at least 50 percent open 
and when the corridor is entirely of noncombustible construction.
 
The use of the plywood disqualifies the exterior projection as being entirely 
constructed of noncombustible or limited-combustible materials or 
fire-retardant-treated lumber, so section 8.15.7.2 and 8.15.7.4 cannot be used. 
If the EIFS system meets the definition of “limited-combustible,” then 
sprinklers can be omitted if the channels are compartmentalized into 160 ft3 
volumes per 8.15.7.3(2) or if sprinklers are provided within the combustible 
concealed space per 8.15.7.3.