On Nov 17, 2010, at 1:40 PM, Singer Wang wrote:

> -  assuming a 10KW load which is not unreasonable given HVAC included and a 
> dozen servers

There's your first false assumption -- Go back to his second message.  His 
total load is less than 20A.  HVAC has been measured at roughly 115VAC/10A, and 
everything else at ~115VAC/8A.

That makes the output results a lot easier to deal with.

> -  Lead-Acid has an energy density of ~40Wh/KG 
> -  so you need at least a 250KG battery per hour
> -  at 8 hours you're looking at at least 2000KG alone for the battery (at 
> least)
> 
> I'd recommend a battery + generator solution....

Again, go back to his second message -- there is absolutely no possibility of 
being able to install a generator of any kind.

--