Thanks Brad, I missed that reply.

Revising based on that the numbers you have, then you're still looking at
400KG+ of batteries in the absolute best possible case..

Singer

On Wed, Nov 17, 2010 at 3:17 PM, Brad Knowles <[email protected]>wrote:

> On Nov 17, 2010, at 1:40 PM, Singer Wang wrote:
>
> > -  assuming a 10KW load which is not unreasonable given HVAC included and
> a dozen servers
>
> There's your first false assumption -- Go back to his second message.  His
> total load is less than 20A.  HVAC has been measured at roughly 115VAC/10A,
> and everything else at ~115VAC/8A.
>

> That makes the output results a lot easier to deal with.
>
> > -  Lead-Acid has an energy density of ~40Wh/KG
> > -  so you need at least a 250KG battery per hour
> > -  at 8 hours you're looking at at least 2000KG alone for the battery (at
> least)
> >
> > I'd recommend a battery + generator solution....
>
> Again, go back to his second message -- there is absolutely no possibility
> of being able to install a generator of any kind.
>
> --
> Brad Knowles <[email protected]>
> LinkedIn Profile: <http://tinyurl.com/y8kpxu>
>
>
_______________________________________________
Tech mailing list
[email protected]
https://lists.lopsa.org/cgi-bin/mailman/listinfo/tech
This list provided by the League of Professional System Administrators
 http://lopsa.org/

Reply via email to