On Thu, Sep 30, 2010 at 11:25 AM, Doug Hughes <d...@will.to> wrote:

>  Unfortunately, the most likely time for a PSU to fail is the stress caused
> during a sudden change in state. This usually happens when the machine has
> been running for a couple/few years, you lose power, it comes back on, has
> 50A of inrush current for .1 seconds, then *pow*. But it can happen during
> failover, as you found too.
>
> You could try asking the vendor for failure stats and if there are any
> particular lot/revision numbers of PSUs that have this issue since it hit
> you a lot. You could do some of this yourself by looking at the model number
> on the replaceable unit. Many times they'll have a rev like A, B, C, etc.
> You can check to see if there's any commonality and then ask the vendor. If
> you don't get anywhere, you could try demanding replacement for all of the
> same model number/rev.
>

That's a good idea. Only 2-3% of the servers failed so I think we'll be able
to narrow it down.


Are you still under service coverage?
>

Yes. For the machine that failed we're going to replace the PSUs, that
should not be a problem.


-- 
Giovanni Tirloni
gtirl...@sysdroid.com