On Sun, 9 Aug 2009 Robert Darlington wrote >I use a 100 pound APC UPS (Smart-UPS 2200XL) that I was given a few years >ago. I suspect it will run a thunderbolt for a month. Check eBay and you >can probably pick one up cheap.
>-bob I tried to use a Trust UPS to transport a GPSDO for a demonstration so that I would not have to wait for the warm up and stabilisation period. The attempt failed because the UPS cut out after a few minutes despite the UPS being proven capable of running a 60 Watt light bulb for an hour. After emailing the distributors it turned out that the unit was designed to cut out if the load was not high enough. The 8 Watts the GPSDO used was not enough in this case despite the UPS theoretically being able to support it for over 7 hours. You may need to check out the specification of the UPS to see that the minimal loading will not be a problem if you are looking for a long support time from a UPS. Regards Malcolm G0MIC _______________________________________________ time-nuts mailing list -- [email protected] To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts and follow the instructions there.