Pardon me for interloping...

One of the ways that I've always explained this is to draw a schematic, actually more of a pictorial of the ground system and each piece of equipment in the overall system as a block. In place of the wires to ground, I draw a resistor symbol, including the ground and ground lead itself. In fact, each chassis or cabinet is also one of the resistors. By looking at it this way you can see that the ground system path is nothing more than a low resistance voltage divider, actually a current divider between a strike and the good earth.

When I design a broadcast transmitter plant I avoid bringing coax (connected to the ground system) in at one end of the transmitter cabinet and the ground connected to the other end of the cabinet, which creates a path where the lightning surge current passes through the cabinet/chassis and everything in between. Instead, I try and tie the ground system and transmission lines - actually all ins and outs to the transmitter, at one end only. This is in addition to the grounding plate as described earlier in this thread. You want to avoid putting any equipment between ground and the lightning strike.

Hopefully the lightning ground conductors and connections are sufficient to not blow apart and allow the remaining force of the strike to find another path. I've seen where heavy wide straps in ground systems were soft soldered together. This is akin to putting a fuse in the ground path.

As a friend once told me, "Lightning never strikes the same place twice because the same place isn't there twice". You want to layout and install your ground system so that your "place" has a better chance of being there after such a spectacular event.

Burt, K6OQK

At 10:19 AM 10/4/2009, [email protected] wrote
From: "Poul-Henning Kamp" <[email protected]>
Subject: Re: [time-nuts] GPS antenna and lightning

Bob Paddock writes:

>I had one strike here that came *up* out of our 300 foot deep water well,
>when a tree several hundred yards away took a direct hit.  You would
>think a 300 foot deep metal pipe filled with water would be a good ground...

The problem is that the ground is not always a good ground...

Burt I. Weiner Associates
Broadcast Technical Services
Glendale, California  U.S.A.
[email protected]
K6OQK