On 28/12/12 23:40, Ken Duffill wrote:
On 27/12/12 23:22, Magnus Danielson wrote:
Sometimes when you have isolated machines, the absolute time may not
need to be very accurate, but the relative timing between them can be.
Adjusting from wrist-watch every once in a while may suffice for
absolute time.

Yes, but what happens to the relative time when you adjust one of the
machines?

It takes time to propagate.

The requirement seems to be to have a deviation of less than 10ms, but
using a wristwatch is only going to give about a second resolution, so
there could be a step change a couple of orders of magnitude bigger than
that whilst the new time is propagated to subordinate machines.

Surely, either don't bother (ever) to resynch to real time, or the
problem remains. Wherever you get the master time from, you must be able
to get it with a resolution of 10ms or better and you must measure how
frequently you need to update the time so that the deviation is never
greater than 10ms at resynch time.

Actually no.

You can have a real time requirement of the nodes in this isolated system to be accurate to about a minute, but a relative timing within the system to be within 10 ms. That is to say, it's OK that both node A and B are 17 s off, if they agree with each other within 10 ms. Consider these equations:

TE_A = T(A) - T(UTC)
TE_B = T(B) - T(UTC)
TE_AB = T(A) - T(B)

If the isolated system only needs to agree within itself to be within +/- 10 ms, then the difference of each of the nodes to proper time (UTC in this case) can be way off mark. If it needs to be brought back to reasonable errors (to compare logs to other logs), then either record the time-difference or during maintenance window adjust the master of those nodes, let the slave jump into place and then continue operations, or at least log the adjustment event and expect the jump.

If you have a very sensitive and 24/7 operation, then just log the difference with outside time and if needed adjust your log times with the logged differences as you present the logs in offline processing.

There is nothing wrong with running an isolated system on it's own time, it just creates the problem of correlating things in outside time, and that creates the need for calibration logs and calibration measurements (without adjusting). There is many ways to achieve the traceability (legal or just layman).

Cheers,
Magnus