I just checked the HP manual, most of the linear equipment is specified: 240V 
+5/-10%
So, I am a little over at 258V here ):
I am going to unplug everything until I can get this sorted out.
Can't afford to lose anything more, in both time and spares obtainability.


marki



-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf 
Of Jim Lux
Sent: Sunday, 7 July 2013 8:01 AM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] HP 5370B Leds pulsing slowly, buttons selecting 
normally, PB LEDS scannning and appears to be reading o/k

On 7/6/13 2:46 PM, Mark C. Stephens wrote:
> Hopefully HP Voltage "Derated" the Cap as well  so it can handle our 
> 250V here.. We are across the road from the main transformer for the 
> area so the voltage is highest at our place, I checked the meter box 
> this morning - it is 255-258V on all 3 phases, no wonder I am having 
> problems.
>


Is that nominally 240 phase to neutral/ 415 phase to phase.  typically, the 
utility is allowed 10% tolerance.. I see that wikipedia says AS60038 calls out 
230V +10% -6% so that's 253 to 216

One thing to be wary of is that the utility supplies voltages at, say, 120V or 
240V (in the US), but utilization equipment (motors, for
instance) is labeled as 115V or 230V.  This accounts for the 2% voltage drop in 
the branch circuit, among other things.



_______________________________________________
time-nuts mailing list -- [email protected] To unsubscribe, go to 
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


_______________________________________________
time-nuts mailing list -- [email protected]
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Reply via email to