This resonates with me somewhat since I used to run nuclear power plants and 
operate the actual turbines.  It does seem that the time interval measurements 
have much more jitter than I would expect.  I suspect the thousands of turbines 
phase locked may introduce all kinds of very subtle variations.  I do know when 
you put a submarine turbine on shore power (grid). You no longer have to 
control speed... The grid does that for you.

Sent from my iPad

> On Nov 16, 2013, at 9:35 PM, Charles Steinmetz <[email protected]> wrote:
> 
> tvb wrote:
> 
>> I think we agree. Just to clarify...
>> 
>> I rely on no hardware and no software filters when I use a time-stamping 
>> counter such as a sub-nanosecond Pendulum CNT-9x or sub-microsecond picPET. 
>> An electrical zero-crossing happens when it happens. If you "filter" you're 
>> just trying to change history: spikes are spikes; noise is noise; history is 
>> history. Deal with it. Record it, don't filter it away.
> 
> Well, it depends on what one wants to investigate.  The "naked" history one 
> captures with no filtering may not be the cleanest history available of the 
> phenomenon under investigation.  Except in unusual circumstances, mains 
> voltage is generated by massive rotating machinery -- so anything fast that 
> happens on your incoming mains voltage is not a reflection of the grid 
> frequency.  If what you want to know is the grid frequency over time (vector 
> sum of the rotational velocity of the various generators on the grid, as seen 
> from your location), a filtered and limited signal may (probably will) 
> provide the best assessment.  Note that local zero crossings are only a proxy 
> for grid frequency to begin with -- and not a very good one, specifically 
> because of the high noise level.  Of course, you can always filter in 
> software if you time-stamp each zero cross in all its naked glory, but 
> removing the noise prior to time-stamping is often preferable to digitally 
> processing a noisy capture.
> 
> Put another way, the massive rotating machinery that generates the mains 
> voltage can only change the zero cross of the grid by a tiny amount from one 
> cycle to the next.  If a data capture method shows cycle-to-cycle jitter that 
> is significantly greater than this amount, the increase cannot be due to the 
> generators, it can only be due to noise.  If one's interest is the grid 
> frequency, removing this noise prior to time-stamping can only help.
> 
> Note that I'm not talking about a filter Q in the millions -- I'd probably be 
> inclined to use a linear-phase filter with several Hz bandwidth, after a more 
> rigorous analysis of the application.
> 
>> You can either focus on the signal, or the noise. That's two separate plots.
> 
> Agreed.  If you are investigating incidental noise on the mains rather than 
> the grid frequency, then the signal you capture needs to be at least as 
> broadband as the noise in which you are interested.
> 
> Since I do not use the actual local mains zero crossings for anything (other 
> than electronically switching loads on at zero voltage and off at zero 
> current, where absolute timing is irrelevant), I'm not sure why one might be 
> interested in characterizing them.  OTOH, since I do have equipment that 
> responds to the grid frequency, I can see practical utility in characterizing 
> that.  Hence my suggestion to filter.
> 
> Best regards,
> 
> Charles
> 
> 
> 
> _______________________________________________
> time-nuts mailing list -- [email protected]
> To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
> and follow the instructions there.
_______________________________________________
time-nuts mailing list -- [email protected]
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.