In message <[email protected]>, Bob kb8tq writes:

>If we want to hold the oven at some temperature +/- 0.1 C, the control loop 
>needs to go from full on to full off over that range.

...ehhh, what ?

>You will map (somehow) the full range of the output into a 0.2 C input range. 

Uhmm... no ?

The full DAC range maps to the heat you need for supply at the two
ambient temperature extremes.

For instance if you were building a -40...+70C OCXO, *ideally*
DAC code 0 should correspond to +70C and DAC code 65535 to -40C ambient

That means that one DAC step corresponds to a change in ambient temperature
of (+70 - -40) / 65536 = 1.7 milliKelvin.

A more realistic temperature range for a time-nut build would be +10...+40C.

        DAC bits        mK
        --------------------
        10              29.3
        12               7.3
        14               1.8
        16               0.5
        --------------------

10 bits would cause I-hunting in your PI(D) but the measurement noise
would probably dither that for you.

12 bits would allos a trivial implementation.

If you go for a double or tripple oven/dewar design, you probably
need 14 bits.


-- 
Poul-Henning Kamp       | UNIX since Zilog Zeus 3.20
[email protected]         | TCP/IP since RFC 956
FreeBSD committer       | BSD since 4.3-tahoe    
Never attribute to malice what can adequately be explained by incompetence.
_______________________________________________
time-nuts mailing list -- [email protected]
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Reply via email to