I have here a pair of instruments that were part  of a system used  at one time 
 in a power station here in NZ  to control the time error in one  part of the 
national grid. It controlled the selected generators and provided a real time 
display of the time error between a reference standard and the 50 Hz mains 
frequency.  The system comprised an HP 5280A reversible counter  with two 
inputs, one from the  mains 50 Hz as generated and one from the reference 
standard. These two inputs were arranged to add  counts from one input and 
subtract counts from the other, such that the counter displayed zero while the 
generated 50 Hz was accurate. Offsets from 50Hz were displayed as positive or 
negative counts. The reference input was derived from an HP 105A quartz 
oscillator and the system included provision to manually  synch that to the 
national standard time standard on an as required basis. The output of the 
5280A counter drove an HP 6933B D/A converter, the bi-polar DC output of which 
was used (both magnitude and sign)  to control the governors on some of the 
hydro generators. Dual HP 5321B clocks were used to display TOD from both 
sources.
 The 6933B is complete but the 5280A counter has been partly disassembled.  The 
5321Bs never got this far-neither did the 105A- who knows, it might still be 
being used  as a reference!

DaveB, NZ

-----Original Message-----
From: time-nuts [mailto:[email protected]] On Behalf Of Bill 
Hawkins
Sent: Monday, July 08, 2019 06:48
To: Bob via time-nuts
Subject: Re: [time-nuts] A Research Proposal

Group,

We've discussed this before, but maybe it needs to be said again.

Line frequency is not constant.   There is no master PLL.  Approximate 
frequency is maintained by a central power dispatching office in each of the 
four (?) regions tied together by their power distribution grid.  The 
dispatcher's goal is to create the same number of cycles of AC each day.  IIRC, 
power is bought and sold by the number of cycles generated.   As the daytime 
load increases, the generators slow down a bit.  Note that it is not possible 
for each generating station to control its frequency, as that would not be 
stable.  Instead, the dispatcher asks various plant operators to generate more 
or less steam (or water flow) in order to increase the frequency.  When the 
load drops at night, the generators speed up a bit, and steam has to be 
reduced. At the end of the day, so to speak, the number of cycles generated is 
very nearly equal to the number generated if the line frequency had been steady 
at 60 (or 50) cycles per second.  Synchronous clocks stay accurate although 
they may be off by a few seconds as dispatchers scramble to get enough steam to 
keep up.

So yes, you can get phase data within a region but you must compensate timing 
data as the frequency varies.

The regions are connected to each other for purposes of power sharing with DC 
transmission lines.  These use inverters to convert between AC and DC. The AC 
frequency is controlled by the grid that it is tied to.  Phase angle can be 
changed to change the amount and direction of the power transferred.

So no, you can't compare data from different regions, unless you want to know 
which way DC power is flowing.

I hope this was informative.

Bill Hawkins


On Thu, Jul 4, 2019, at 2:00 PM, Andy Backus wrote:
> Historically, and even today, the steady frequency of AC power has 
> been used for timekeeping.  So there may be interest here in the 
> following research proposal:
> 
> Within a given power distribution grid, several observers as widely 
> separated geographically as possible, time stamp the first two zero 
> crossings of the power line after each UTC second – over the course of
> 24 hours (86,400 pairs of data).
> 
> Popularly conceived, all the components of a power distribution grid 
> are phase locked – though, of course, power is taken in and out by 
> varying degrees of lead or lag.  Frequency is maintained by a constant 
> balancing act between load and generation.
> 
> Typical power distribution grids, however, are sized on a scale of 
> thousands of miles.  “Locking phase,” then, is problematic simply on 
> the basis of the limits of information transmission rate.  Even at c, 
> every 1000 miles takes 5 ms, which represents a third to a quarter of 
> the period of the AC power waveform.
> 
> Many interesting phenomena might result from that reality, which 
> suggests a certain constrained flexibility over large distances – 
> almost as if the system is like a large lake of viscous liquid.  When 
> there are local disturbances such as rapid load changes or sudden 
> generation adjustments, for example, it is quite possible harmonic 
> ripples could be propagated through the system.
> 
> Such effects could be observed by comparing phase data across 
> significant distances within a distribution grid.
> 
> Andy Backus
> Bellingham, WA
> USA
> 
> ________________________________
> From: time-nuts <[email protected]> on behalf of Thomas 
> D. Erb <[email protected]>
> Sent: Thursday, July 4, 2019 5:23 AM
> To: [email protected]
> Subject: Re: [time-nuts] 60 Hz frequency and phase measurement
> 
snip
> I had a recent tour of a power station - the operators had no idea the 
> output was synchronized to a time standard - they just synchronize 
> with the local grid.

> 
> Thomas D. Erb
> p:        508-359-4396
> f:        508-359-4482
> a:        97 West Street, Medfield, MA 02052 USA
> e:         [email protected]
> w:        www.electrictime.com<http://www.electrictime.com>
> Tower & Street Clocks Since 1928
> 

_______________________________________________
time-nuts mailing list -- [email protected] To unsubscribe, go to 
http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com
and follow the instructions there.



_______________________________________________
time-nuts mailing list -- [email protected]
To unsubscribe, go to 
http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com
and follow the instructions there.

Reply via email to