Try https://en.wikipedia.org/wiki/PID_controller

If that doesn't help, what we used to do for industrial process controllers was 
to set Reset time to the largest value and Derivative to zero (to disable them) 
and then increasethe gain until the loop oscillated when you made a step change 
to the setpoint, then you used 70% of that value for gain. The period of 
oscillation told you how to do Reset, but I don't remember that. Conservative 
settings were used because control valves were not linear. Heaters are 
generally linear.

Bill Hawkins, whose memory isn't what it used to be.

On Sat, Mar 7, 2020, at 5:04 PM, Hal Murray wrote:
> 
> [email protected] said:
> > As far as I know there is no “closed form” solution to tuning a GPSDO. It is
> > very much a measure / tweak / measure / tweak sort of thing. 
> 
> I've seen a recipe for tuning a PID controller. That was ages ago. I wonder 
> where.
> 
> The key idea was that you needed to be able to poke the system and see how it 
> responded.
> 
> Google for >tune PID< gets several hits that might be worth investigating.
> 
> 
> -- 
> These are my opinions. I hate spam.
> 
> 
> 
> 
> 
> _______________________________________________
> time-nuts mailing list -- [email protected]
> To unsubscribe, go to 
> http://lists.febo.com/mailman/listinfo/time-nuts_lists.febo.com
> and follow the instructions there.
> 