Hi Dave,

According to Annex B of ETSI document EG 201212 "Electrical safety; 
Classification of interfaces for
equipment to be connected to telecommunication networks":
"48 Volt" Station Battery is to be considered as SELV where Vmax =< 57Vdc.
"60 Volt" Station Battery is to be considered as TNV-2 where Vmax =< 75Vdc.

As Ed described the input as going up to 72Vdc, then, IMHO, this circuit should 
be classified as
TNV-2 with the above reference and with the TNV-2 circuit definition found in 
IEC/EN/UL60950. Also
see clause 5.3 of EG 201212 for user information recommendations.

The above assumes that Ed's product connects to a telecommunication network.

Please note that as the EG of EG 201212 refers to "ETSI Guide" (see the 
foreward), its hardly a
regulatory requirement, however, it is a useful document that provides guidance 
for the
classification of most TNV type circuits. And, it can be downloaded for free 
from the ETSI site.

I hope this helps clarify this issue. Comments?

Best regards,

Ron Pickard
[email protected]




                                                                                
                                            
                    [email protected]                                      
                                            
                    Sent by:                       To:     
[email protected]                                           
                    owner-emc-pstc@majordom        cc:     [email protected], 
[email protected]                            
                    o.ieee.org                     Subject:     Re: TNV-2 to 
Earth requirement                              
                                                                                
                                            
                                                                                
                                            
                    01/17/02 02:33 PM                                           
                                            
                    Please respond to                                           
                                            
                    daveheald                                                   
                                            
                                                                                
                                            
                                                                                
                                            





Does your equipment plug into a primary (AC) circuit?  Any TNV circuit
is considered a secondary circuit and if any and all power is derived
from the TNV network, the notes you referenced would not apply as a
primary circuit is not present.

Best Regards,
Dave Heald

Ed Eszlari wrote:
>
> All,
>
> I have a DC to DC "filter" which is rated 32 - 72 VDC input and output
> which I am considering to be TNV-2 according to EN60950/IEC60950 2nd
> edition.
>
> This filter has a metal chassis which is earthed, and it will be
> installed in a service access area only by qualified service
> personnel. It is not permanently connected or pluggable type B, and
> does not have a provision for a permanently connected earthing
> conductor. With all this considered, it seems that Norway and Sweden
> are the only Countries that require Supplemental insulation for a
> primary circuit between this TNV-2 circuit and earth.
> Is there any way around this requirement due to this filter operating
> at 72VDC and not being directly connected to mains?
>
> Any help would be appreciated.
>
> Ed
>
> ----------------------------------------------------------------------
> MSN Photos is the easiest way to share and print your photos: Click
> Here
> ------------------------------------------- This message is from the
> IEEE EMC Society Product Safety Technical Committee emc-pstc
> discussion list. Visit our web site at:
> http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription,
> send mail to: [email protected] with the single line: unsubscribe
> emc-pstc For help, send mail to the list administrators: Michael
> Garretson: [email protected] Dave Heald [email protected]
> For policy questions, send mail to: Richard Nute: [email protected] Jim
> Bacher: [email protected] All emc-pstc postings are archived and
> searchable on the web at: No longer online until our new server is
> brought online and the old messages are imported into the new server.

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into
the new server.





-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to