I must be reading a different version of IEC950/EN60950.   Table 6 shows 
the creepage distances to be the same for basic or suplementary insulation. 
 In the UK, in the absence of the CTI rating, Pollution degree 2/material 
group III is assumed. We therefore have a CR/CL of 2.5mm.

The UK labs also consider the port for connection to other pluggable type A 
apparatus (PC for example) which would invite the connection of a SELV 
circuit to P.E.   Supplementary insulation is then required between TNV and 
circuitry that may be earthed, either within the equipment under test OR 
VIA OTHER EQUIPMENT (Ref. Clause 6.3.3 of IEC950)

Best regards
Barry Singleton
Approvals Specialist
-------------
Original Text
From: Jon D Curtis <[email protected]>, on 01/10/96 14:53:
From: Dan Roman <[email protected]>
Reply-To: [email protected]
Organization: Dialogic Corporation
X-Mailer: Mozilla 3.0Gold (WinNT; I)
Mime-Version: 1.0
To: [email protected]
Subject: Re: Printed Circuit Board Layout
References: <[email protected]>
Content-Type: text/plain; charset=us-ascii
Content-Transfer-Encoding: 7bit

Doug,

There seem to be some confusing responses being returned to you.  I'll
offer one more response but I suggest you contact the lab (UL I assume)
that is going to be doing the testing for you before you etch the
boards!

Throughout most of the world E1 is considered SELV so the quotes you
received for supplementary insulation @ 240 Vac, 2.5 mm between TNV and
SELV or Earth and 1500 V dielectric, only apply to loop/ground start
interfaces and not to a "digital" interface like yours.

Having said that, T1 interfaces come in two flavors, DSX-1 and DS1. 
DSX-1 is SELV, "short haul", supposed to be behind a registered CSU
(which gives the safety protection), in-building wiring.  DS1 has the
CSU built-in and is TNV, "long haul", goes outside of the building on
the pole or underground with the AC wiring.

My experience with UL has been that DSX-1 is treated like SELV (no
testing) and DS1 like TNV which requires overvoltage testing,
dielectrics, and creepage and clearance.  I believe also that UL's
requirement is basic insulation between TNV and SELV or Earth which
still means 1500 V dielectric but only 1.6 mm creepage and clearance but
it has been quite awhile since I did a CSU application so as I said,
check with them first.

BTW, they have no requirement for T/R or T1/R1 spacing and for EMI
purposes I would route each tip and ring pair as closely as possible to
each other (they are differential signals after all).