     Doug,
     
     Looks like Table 4-6. "Equipment Area Heat Release Objective" as 
     described in GR-63-CORE is what you want.
     
     The answer depends on if forced air is used or not, if it is an 
     individual frame, multiframe, or shelf.
     
     From what you've said, your category is individual frame:
     Natural Convection.. 134.7 W/sq. ft.
     Forced Air...........181.2 W/sq. ft.
     
     
     In calculating area, you are allowed half of the front and rear aisles 
     as well as the equipment space.
     
     
     Eric Petitpierre
     Pulsecom
     Herndon, VA
     [email protected]


______________________________ Reply Separator _________________________________
Subject: Bellcore Requirement
Author:  [email protected] (Doug McKean) at SMTP
List-Post: [email protected]
Date:    8/11/97 11:55 AM


What is the Bellcore requirement for something 
like watts per square foot in a CO?  It's based 
on looking down on a rack from above so that 
you get "watts per square foot".
     
My memory lags on this, and I believe its 
TR-499. But, I remember going through 
some numberical contortions to figure
it out for a standard 17' rack. Somehow 
650 watts per square foot for a standard 
17' rack keeps popping into my mind.