Many other standards state that voltage shall decay under a safety level
(i.e., 60 V). However, to measure it is necessary to cut the power just
in the top of the wave, and it is difficult. If we speak about
percentage, that problem won't exist: the decay time until 37% of it
initial value depends only on the time constant of the circuit,
independently of the initial voltage.

But you are right and that definition may force an excessive
requirement. Maybe,  the best option could be to mix both methods.

Juan P. Pena            /       Electrical Safety Area
Company: CETECOM, S.A. (http://www.cetecom.es)
e-mail: [email protected]


        ----------
        De:  Munechika Gomi[SMTP:[email protected]]
        Enviado el:  viernes 3 de octubre de 1997 8:35
        Para:  EMC-PSTC
        Asunto:  Capacitor discharge: IEC950 2.1.10

        Would anyone tell me why IEC950 allows a capacitor having a
discharge means
        in a time constant not exceeding: ---, i.e. during one
time-constant the
        voltage decays to 37 % of its original value?

        The reason of my question is:

        If the original voltage is 120 V ac, 37 % or its original will
exceed 60 V
        dc which I think is hazardous in terms of voltage.

        Is there any implied consideration in IEC950 for energy level
other than
        voltage?

        Thank you for your help in advance.

        Mike Gomi 