Thanks for all the good feedback and questions you have kindly submitted -
I have the following new information.

I found the person responsible for maintaining the HiPot system and, (to my
surprise) he can not remember any report of a shock or injury at the HiPot
tester except for a close-call several months ago where horse-play was
involved.  I just discussed this with the plant safety officer and
apparently this is a case where the story got worse each time it was
repeated.  So while there may be a hazard, there is no documented case of
injury within memory of the HiPot supervisor or any formal injury report
given to the safety officer.  However, there was some useful discoveries
made nonetheless.

The tester is an aging Rod-L system composed of three units: a model M150AC
HiPot tester (cal is current), a model M30 ground continuity tester (cal
also current), and a GPIB controller module.  Only the M30 carries the UL
label, none was found on the M150AC HiPot generator.  The entire system is
controlled from a recently redone in-house application on a PC, the new PC
application allows HiPot failures to be immediately logged into the
production database.

This system requires a two-step operation, continuity and hipot, by
manually replugging the power cord into each instrument.  The test order
was not established in the time I had available (other meetings...).

The system shares workspace with other manufacturing and test functions,
placing the operator potentially elbow-to-elbow with co-workers, and
placing them at some risk of injury.

The HiPot tester does not appear to have a specific ground check safety
feature, no evident warning indicator exists on the HiPot unit itself
(aside from pass/fail) - but the M150AC user manual is currently
missing....

According to the M30 manual, the continuity tester is wired to the M150AC
correctly.  A new ground clamp and cable was added recently to replace the
original one that was nearly falling apart, and it appears to be well
built.

This system fails HiPot on occasion, while the same products subsequently
pass on a portable HiPot tester that also bears a current calibration
sticker.

All this, and we're about to open another production line....

Next Steps

The entire tester will be moved tomorrow to a new dedicated bench with the
floor space clearly set-off by safety yellow/black tape (only the operator
is permitted to enter).  Some colorful High Voltage warning signs will also
be posted above the workspace.

Written procedures exist (as per ISO 9002) but they need to be reviewed;
and I will recommend augmenting the written procedures with a video
training tape.

I have concluded that this system is too old, can't support our increasing
manufacturing volume any more, and is now a liability (read that PITA). I
have decided to call for the ASAP purchase of a new modern test system; the
safety officer and the HiPot supervisor appear to be happy with the idea.
Management is expected to heartily endorse the proposal.

Best Regards,
Eric Lifsey
National Instruments






[email protected] on 01/08/98 10:53:47 AM

Please respond to [email protected]

To:   [email protected]
cc:    (bcc: Eric Lifsey/AUS/NIC)
Subject:  HiPot Testing - Operator Safety Precautions?




We're looking into a problem where, on occasion, our manufacturing
operators are getting zapped while operating a production HiPot test
station.  (Just how this happens is yet to be determined.)  I've reviewed
literature on HiPot equipment, but nothing I have suggests any operator
safety features are available.  I can imagine some simple methods to
prevent this, but I thought it might be worth soliciting ideas from those
that have successfully solved this particular problem, since it may be a
more common problem than most of us realize.