I have a lot of experience with hipots and their use in the lab and on the 
assembly line.  However, your note has no evidence to get one started.  Go to 
the assembly line and interview the operators.  Ask specifically what they were 
touching when they got the shock.  If you let me know what you learn I can 
probably start you off in the correct direction.  Also tell how the connection 
is made between the hipot and the product.  Hipots vary from simple 
transformers 
to sophisticated processor controlled testers, so give me some idea of what you 
are using.  If the hipot is a current limited tester (in the 10-30mA range) you 
can take a reasonable time to correct the problem. If the hipot is one that 
will 
maintain full output under a fault, I recomment that you stop the factory from 
using it until the situation is corrected.

Best Regards, Lou Aiken
<---- Begin Forwarded Message ---->
From: [email protected]
To: [email protected]
List-Post: [email protected]
Date: Thu, 8 Jan 1998 10:53:47 -0600
Subject: HiPot Testing - Operator Safety Precautions?
Reply-To: [email protected]

We're looking into a problem where, on occasion, our manufacturing
operators are getting zapped while operating a production HiPot test
station.  (Just how this happens is yet to be determined.)  I've reviewed
literature on HiPot equipment, but nothing I have suggests any operator
safety features are available.  I can imagine some simple methods to
prevent this, but I thought it might be worth soliciting ideas from those
that have successfully solved this particular problem, since it may be a
more common problem than most of us realize.

Regards,
Eric Lifsey
Compliance Engineer
National Instruments