Hi Glenn:


Thanks for your questions...

>   Both cl 1.2.5.1 and 1.2.5.2 say ...plug and socket-outlet OR an
>   appliance coupler OR both.  If my product uses an IEC320 plug for the
>   wall, and an IEC309 ac inlet to the product, is it type A or B?

The issue is high leakage current.  Because the leakage 
current is high (i.e., more than 3.5 mA and therefore 
potential injurious), the connection to ground must be
assured by the choice of connection to the supply (and
thereby the connection to ground).

High leakage current requires a high-integrity ground.  A
high-integrity ground is provided by industrial grade plugs
and sockets such as those in IEC 309.

Ordinary plugs and sockets such as those in IEC 83, and 
appliance couplers specified in IEC 320, do not provide a
high-integrity ground as required for high leakage currents.

You propose to use an IEC 309 high-integrity ground plug in 
one location, and then convert to a different (low-integrity 
ground) plug (IEC 320) at another location.  

This defeats the high-integrity ground provided by the IEC 
309 plug.


Best regards,
Rich


ps:  You can't use an IEC 320 plug for the wall.  IEC 320 
     devices are, by definition, appliance couplers.  They 
     are ALWAYS located at the load end of the power cord, 
     not the supply end.

     If you are using an IEC 320 plug, then you are plugging 
     it into an IEC 320 outlet located on another piece of 
     equipment or multiple outlet strip.  You are NOT 
     connecting to the building supply.

Reply via email to