Dear All,

I'm trying to make sure that some conductors carrying 230V r.m.s in an
ambient temperature of 70oC have a large enough conductor and the
correct insulation to withstand a short circuit current of 17A for 30
minutes.

Does anyone know which formulae are appropriate?

I have tried the calculations in BS7454 : 1991 "Calculations of
thermally permissible short-circuit currents, taking into account
non-adiabatic heating effects" and the results don't seem to make sense.

So here are the parameters

Max current = 17A
Start temp - 20oC
Conductor size - 1.5mm2
Time period - 30 mins
Conductors not bunched

I'm trying to find out what the final PVC insulation temperature will
be, all the catalogues that I have only seem to give the current at 20
or 30oC.

The results I have are:
Adiabatic - 23291.48oC
Non-adiabatic - 34.48oC

The results are supposed to give the final temperature. For the
non-adiabatic result, is a 14oC rise what you would expect or is this
the
whole rise 20 + 34.48 = 54.48oC?


Are there any wire experts out there?

Regards

Richard