-------------Forwarded Message-----------------

From:   INTERNET:[email protected], INTERNET:[email protected]
To:     , INTERNET:[email protected]
        
List-Post: [email protected]
Date:   5/19/99  9:53 AM

RE:     Re: overvoltage protectors to ground


Dwight:

As revealed in other responses to your inquiry, there are not so obvious return
paths for the fault energy including the 'isolated' paths through optocouplers,
transformers, etc.  Once a 3-legged approach  is decided upon, consideration
should be given as to how it is implemented.  Using item 2 below with 2 devices
in series and 3rd leg to ground results in a higher protect voltage across T-R
than on each leg to ground.  Adding a 3rd device in the ground lead can even
this out but this whole approach can result in unmatched breakover voltages as
well as the expense and realestate of multiple parts.  3 leg devices are
available that have balanced OVP built-in.  Teccor comes to mind.  Depending on
your design, some of these later devices are capable of handling surges without
a current limiting device.  There is also a 3 leg device which combines the
tremendous current sink capability of a gas tube and the speed/predictability
of solidstate switching.

Finding a good ground point can also be a challenge.  Plug-in cards and
portable equipment present special cases.  Ideally, these surge currents should
be directed to chassis/earth ground.  If some other ground point has to be
utilized, do the layout to avoid having the surge currents pass through other
more sensitive circuitry ground returns.

At 10:23 AM 5/18/99 -0700, you wrote:
>Question regarding "two-legged" vs. "three-legged" overvoltage
>protection circuitry: What are the pro & cons of the two? 
>
>Background: Typically, to protect against overvoltages on a telco
>interface protection circuit (analog or digital, such as POTS, T1, HDSL,
>etc.), one sees either:
>
>1) an MOV/varistor type device across TIP/RING, or
>2) two MOV/varistor/gas-tube type devices tied in series across
>TIP/RING, with the center connection tied to earth ground.
>
>Of course, there are also typically PTC's or fuses in line for
>overcurrent protection.  However, my interest is the pros/cons of the
>overvoltage protection topology.
>
>If the interface circuit has no path to earth (typically through
>overvoltage protectors), then UL1950/UL1459 allows waiving of the
>longitudinal(common) mode overvoltage tests, which makes sense, because
>there is no return path for the fault energy.
>
>Since this waiver eliminates about half of the overvoltage testing, why
>does one see the "three-legged" topology being used?  Are there some
>advantages to shunting energy to earth, rather than just back out the
>TIP/RING pair?  Certainly, one has to provide overcurrent protection to
>prevent building telco wiring from burning (tested via the MDQ 1-6/10A
>fuse), but are there other reasons for preferring a three-legged
>approach? What are you missing out on if you elect to use the simpler
>topology of just an MOV across TIP/RING?
>
>(To further stir things up, how about if we take into consideration
>Bellcore GR-1089-CORE? Does that change things?  I don't believe GR-1089
>specifically contains the same waiver as UL1950/UL1459, but certainly
>the results are the same, and a test lab should consider waiving for the
>same rationale.)
>
>I'm sure many of you have seen both topologies described in application
>notes for various interface components, and have had to deal with both.
>Any light shed will be appreciated by all.
>
>D
>-- 
>
>DWIGHT HUNNICUTT
>Sr. Compliance Engineer
>
>****************************
>*  <[email protected]>  *
>*  (510) 771-3349 direct   *
>*  (510) 492-0808 fax      *
>*  VINA Technologies,Inc.  *
>****************************


Mark Sechler
[email protected]
General Dynamics - Advanced Technology Systems
3801 Boren Drive
Greensboro, NC  27407
Phone:  336/547-3871
Fax:  336/547-7432



----------------------- Internet Header --------------------------------
Sender: [email protected]
Received: from europe.std.com (europe.std.com [199.172.62.20])
        by hpdmgaaa.compuserve.com (8.8.8/8.8.8/HP-1.4) with ESMTP id IAA05374;
        Wed, 19 May 1999 08:53:29 -0400 (EDT)
Received: by europe.std.com (STD1.2/BZS-8-1.0)
        id IAA21266; Wed, 19 May 1999 08:51:59 -0400 (EDT)
Received: from world.std.com by europe.std.com (STD1.2/BZS-8-1.0)
        id IAA21250; Wed, 19 May 1999 08:51:56 -0400 (EDT)
Received: from stingray.gdats.com (client.gdats.com) by world.std.com 
(TheWorld/Spike-2.0)
        id AA28360; Wed, 19 May 1999 08:51:51 -0400
Received: from dnoel.gdats.com ([172.17.17.107])
        by stingray.gdats.com (8.8.8/8.8.8) with SMTP id IAA20024
        for <[email protected]>; Wed, 19 May 1999 08:51:33 -0400 (EDT)
Message-Id: <[email protected]>
X-Sender: [email protected]
X-Mailer: QUALCOMM Windows Eudora Pro Version 4.1 
List-Post: [email protected]
Date: Wed, 19 May 1999 08:53:24 -0400
To: [email protected]
From: Mark Sechler <[email protected]>
Subject: Re: overvoltage protectors to ground
In-Reply-To: <[email protected]>
Mime-Version: 1.0
Content-Type: multipart/alternative;
        boundary="=====================_3082733==_.ALT"
Sender: [email protected]
Precedence: list
Reply-To: [email protected]

Reply via email to