-----Original Message-----
From: Michel Jullian

Thanks Terry. The above is quite right but in the case of typical
rectifier+capacitor loads the low power factor is due to shape rather than phase of the current (brief capacitor refill current pulses at voltage peaks). But this increases RMS current all the same, and RMS current is what heats the wire: Pw=Rw*Irms^2. This is a fact. If you care to reread my previous post in this light you will realize you have unjustly criticized your electrical dudes :)

<><><><><><>

Well, sure, if it deviates from a sinusoid. I was trying to use this as an example. My bad.

I'm sorry for this rant which is really off topic; but, we're facing a real problem in many of our contracts. In our industry, we often must budget five years in advance. In the past five years we have seen tremendous rise in commodity prices. Today Cu is trading at the $3.60 per pound area. This is up from about $1 per pound two years ago.

The NFPA requires branch circuits to be rated for the KVA load which includes real and reactive power. However, reactive power does not contribute to ohmic heating. The NFPA was changed because PF were not always known so they took the safe approach.

Here in the transit industry, we know our PFs for all our loads; however, I can't convince them that they do not have to increase their conductor sized to meet this NFPA requirement. Besides, we're not even subject to the NFPA. Because we're talking hundreds of miles of 750 kcm Cu conductors here, we're talking about millions of wasted $$.

<rant over>