This has been my experience, Scott.

I have seen lightening enter an enclosed device and simply burn a hole right
in the middle of a circuit board with nothing else damaged.

On my desktop PC, lightening apparently came in through the cable, through
the cable modem (destroyed) and down the Ethernet, through the Linksys (OK)
to the PC and the only other damage was the motherboard Ethernet.  I
replaced the modem and bought a PCI Ethernet card and it's fine.  What paths
lightening took in this incident or the above incident is anyone's guess.

There is still controversy over the value of diverting or directing
lightening and/or lightening leaders and streamers to protect against a
direct hit.

It's really fascinating and here's a fun place to start you thinking:
http://en.wikipedia.org/wiki/Lightning_rod

Nevertheless, good enclosures fed with metal conduit that's well grounded
appear to do well but the local ordinances need to be heeded.

. . . j o n a t h a n

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Scott Reed
Sent: Tuesday, May 22, 2007 5:35 PM
To: [EMAIL PROTECTED]; WISPA General List
Subject: Re: [WISPA] FM Radio and Ethernet

If properly grounded, the opposite is true.  The ground wire should 
direct the lightning to ground (hence the name) and away from your 
equipment.

Not to mention that in the case of an equipment failure that causes the 
power supply to put 120VAC on the case, etc., the ground wire directs 
the current to ground, not you.  It is always about safety.  I would 
much rather have dead equipment than dead personnel because an 
electrical system was not properly grounded.

Dennis Burgess wrote:
> YOU DO NOT WANT TO RUN A GROUND WIRE!  The reason for that, is that 
> then it
> gives lightning etc the ability to go though your equipment vs the tower
> ground!  B
>
>
>
>
> On 5/22/07, Scott Reed <[EMAIL PROTECTED]> wrote:
>>
>> Again,
>> Check your local code before you copy this.  No ground is not allowed
>> here, unless somehow you can prove it is a temporary extension cord.
>> Neither is low voltage in same conduit at 120VAC.
>>
>> That said, small changes to Dennis' configuration will make good
>> installation.
>>
>> Run the cat5 in a separate (metallic) pipe (rigid, EMT, Sealtite,
>> whatever you like).  Ground the bottom of the pipe.  I would leave the
>> top ungrounded, but that is:
>>    1) personal preference (eliminates ground loops).
>>    2) determined by which way gives you the best performance, least
>> interference from the FM.
>> You may want to use cat5e or cat6 as the twist is tighter, thus
>> accepting less interference as well.
>>
>> Run a ground wire with the power.  Even for the low current required at
>> the top, I would probably run 14AWG or 12AWG. Lowers the inductance, may
>> allow less noise to be induced on the power leads.   Besides, 14AWG is
>> the smallest wire you can run with a 15amp breaker.  Same thing with
>> ground loops; I would probably use a plastic box and thus isolate the
>> power ground from the enclosure, tower, etc.
>>
>> One good way to do it is consult a local commercial/industrial
>> electrician.  They will know the code for your area.  But they don't
>> always understand radio and induced voltages.
>>
>>
>> Dennis Burgess wrote:
>> > We are located at 400 foot on a FM tower, 100,000 watts at the top of
>> > 1400
>> > foot.
>> >
>> > The total length of CAT 5 is 440 foot or so, and plug directly into a
>> > RB532
>> > at the top of the tower (power at the top as well)
>> >
>> > We ran a felexable conduit up the tower, inside, 16awg solid 
>> copper, one
>> > black, one white, (for the 110), NO GROUND, and also in that same
>> > conduit,
>> > we ran good outdoor, sheilded CAT5, UV Resistant (even though it is
>> fully
>> > enclosed), and we get a 100meg link without issues for the most part!
>> >
>> > One thing we did do, is ensure that we were on the other side of 
>> all the
>> > transmission lines running up the tower.
>> >
>> > Dennis
>> >
>> >
>> >
>> > On 5/22/07, Andrew Niemantsverdriet <[EMAIL PROTECTED]> wrote:
>> >>
>> >> I am co located on a tower with an FM transmitter. The FM station 
>> runs
>> >> at 105Mhz. We were running one AP at 10 half duplex to overcome the
>> >> havoc that the FM station created on our ethernet feed. We now 
>> need to
>> >> run that link at 100 full duplex to be able to handle the traffic
>> >> coming through it. What are some hints tips tricks to make it work.
>> >>
>> >> The cable run itself is 150' of shielded CAT5. It works fine at 10 
>> H/D
>> >> and it works at 100 F/D most of the time but it will occasionally go
>> >> down and there is some intermittent packet loss on that link. The run
>> >> itself terminates into a managed switch.
>> >>
>> >> If CAT5 won't work, is fiber my next option? How does that work? I
>> >> assume that I need power up the tower as well? Any tips to make that
>> >> happen assuming keeping the existing CAT5 won't work.
>> >> --
>> >> WISPA Wireless List: wireless@wispa.org
>> >>
>> >> Subscribe/Unsubscribe:
>> >> http://lists.wispa.org/mailman/listinfo/wireless
>> >>
>> >> Archives: http://lists.wispa.org/pipermail/wireless/
>> >>
>> >
>> >
>> >
>>
>> -- 
>> Scott Reed
>> Owner
>> NewWays
>> Wireless Networking
>> Network Design, Installation and Administration
>> www.nwwnet.net
>>
>> -- 
>> WISPA Wireless List: wireless@wispa.org
>>
>> Subscribe/Unsubscribe:
>> http://lists.wispa.org/mailman/listinfo/wireless
>>
>> Archives: http://lists.wispa.org/pipermail/wireless/
>>
>
>
>

-- 
Scott Reed
Owner
NewWays
Wireless Networking
Network Design, Installation and Administration
www.nwwnet.net

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

-- 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

Reply via email to