On Thu, 2006-07-20 at 15:14 +0200, ROSSIER Daniel wrote:
> 
> Hi all,
> 
> Attached, another tricky piece of code.
> 
> We actually try to exhibit a priority inversion by using the semaphore (which 
> does not implement the priority inheritance protocol).
> 
> We have the three following tasks:
> 
> - meteoDataAcquisition: acquiring the mutex, spinning 10ms, releasing the 
> mutex / priority 1 / delayed at 18ms, and then activated with a frequency of 
> 1000 ms from its first activation (so normally, more or less activated at 
> 1018, 2018, 3018, etc.)
> 
> - busManagement: acquiring the mutex, spinning 5 ms, releasing the mutex / 
> priority 10 / period of 20 ms.
> - comHandling: just spinning 10ms, period of 20 ms.
> 
> So, the worst case would be when the meteoDataAcquisition acquired the mutex 
> right before the busManagement, so we can say that the highest priority task 
> will be delayed of 10ms at the worst; we put an alarm of 30ms, then no alarm 
> will raise up; and indeed, it works like that.
> 
> Doing the same stuff with the semaphore - just change WITH_MUTEX to 0 - 
> should theoretically lead to an alarm since the comHandling will take the 
> hand, delaying the busManagement over 30ms. Here comes the problem: if we 
> leave the alarm at 30ms, the alarm raises up, as expected. But, if we change 
> the alarm to 31ms, there is no alarm anymore... and we do not understand why? 
> Normally we should see some alarms for some values from 31 to 35ms, since 
> comHandling spins during 10ms. Mytery...
> 
> Normally, the task meteoDataAcquisition is aperiodic, and activated on the 
> basis of an IRQ. In order to simulate that, we put the task with a delay of 
> 18ms (yes, that's the reason of 18 ;-)), activated each second (therefore 
> causing the priority inversion systematically). But nothing happens! the 
> system runs, but no alarm raises up with 

With some help from the simulator,
http://download.gna.org/xenomai/screenshots/simulator.png
here is the timeline of your example:

[sys_date*]     [task]  [alarm_setup*]
0               com
10              bus     15
18              mto
20              bus     35
loop:
20              com
40              bus     45
45              com
60              bus     65
65              com
80              bus     85
85              com
100             bus     105
105             com
118             mto
120             bus     135
jump loop

(*) system and alarm setup dates are expressed in relative ticks since
the application startup.

Given that there is never more than 30 ticks between two alarm setups in
this timeline (i.e. between ticks #105 and #135), the result you got
looks correct.

-- 
Philippe.