RE: NEC Questions

2002-05-01 Thread Peter Tarver

Richard -

Bob Johnson's response on your Q1 is on the money.

wrt your Q2 and outlet strips, there may be the additional
consideration that you may impinge on the scope of UL1363,
Relocatable Power Taps (formerly a desk standard for
Temporary Power Taps), Listed under the CCN XBYS.  Point
being, the final assembled product may have to comply with
UL1363, with the internal measurement device having
requirements from UL3111-1.  [This was the case for
relocatable power taps that incorporated secondary
protection for telecommunications circuits, where the
latter, internal components were required to comply with
UL497A.]


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com


 -Original Message-
 From: Richard Meyette
 Sent: Tuesday, April 30, 2002 10:05 AM

 I have a couple of questions regrading the
 National Electrical Code:

 2) Consider the same power measuring circuit
 installed into a direct
 plug-in (NEMA 5-15P) with a single outlet
 receptacle (NEMA 5-15R) or into
 an outlet strip with a 16 AWG power cord with
 several outlet
 receptacles.  Assuming that the measuring circuit
 is provided with a
 suitable fuse for overcurrent protection, are the
 outlet receptacles
 required to be protected by a 15 A fuse or
 circuit breaker in the device or
 can they rely on the circuit breaker for the
 branch circuit for overcurrent
 protection?

 The UL product standard for this device is UL
 3111-1 (Electrical Measuring
 and Test Equipment), which is harmonized with IEC
 61010-1, requires an
 overcurrent protector to be fitted within the
 equipment for all devices
 connected to the mains supply (9.6.2). There are
 no US deviations in this
 standard that would allow the circuit breaker to
 provide this protection,
 so based on this I would assume that a 15 A
 circuit breaker of fuse would
 be required for the NEMA 5-15R receptacles.  I
 would also assume that a 20
 A overcurrent protector would be required for a
 NEMA 5-20R outlet receptacle.

 However, the UL product standard for household
 appliances (UL 60335-1) does
 have a US deviation to a similar requirement for
 overcurrent devices (19.1,
 Note 2) that states the The PROTECTIVE DEVICE in
 the fixed wiring does not
 provide the necessary protection.  However, the
 US deviation states The
 circuit protection device is permitted to provide
 necessary
 protection.  If I am interpreting this
 correctly, a household appliance in
 the USA could rely on the panel breaker for
 overcurrent protection.  Any
 comments?

 Thanks in advance for anyone willing to wade
 through this and send me a
 response.

 Richard A. Meyette. PE
 meye...@pacbell.net




 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:
 http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable
 on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: NEC Questions

2002-04-30 Thread Robert Johnson
1) Correct, this cannot be used in a multiwire branch circuit since it
may eventually be removed without being bypassed. The concern is that an
open neutral in a multiwire (e.g. 120/240 3w or 120/208 4w) circuit
leaves loads connected in series phase to phase. The voltage across a
product intended to operate phase to neutral then becomes dependent on
the other series loads.
Note also that measuring the current in the neutral of a multiwire
circuit will not provide power measurement for any currents flowing
phase to phase. For example when loads on each phase are equally
balanced, neutral current would be zero (ignoring harmonics).
I see no other code complications. I wonder however why you need to make
the current measurement in the neutral rather than the phase conductor.

2) The 15 or 20 amp receptacles must be protected with Listed devices
(not recognized devices such as supplementary protectors). This
protection however may be provided by the branch circuit. If the product
with receptacles has a plug of the same size (e.g. 15 or 20 amps) then
you can assume it is connected to a circuit with the proper protection
and therefore avoid additional protection. If it plugs into a larger
circuit such as a 30 amp receptacle, then you will need to add Listed 15
or 20 amp overcurrent protection within the product for protection of
the smaller receptacles.
Note that UL is reconsidering this requirement, but standards changes
have not been made yet. 
Note also that Canada does not permit 15 amp receptacles on 20 amp
circuits (and therefore does not permit the T-slot type 5-20R
receptacles), although this may have changed recently. Maybe Canadians
can clarify.
My responses are based on UL/CSA 60950, but I think you will find this
subject is consistent across other standards.



Bob Johnson
ITE Safety
 

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of Richard Meyette
Sent: Tuesday, April 30, 2002 1:05 PM
To: emc-p...@majordomo.ieee.org
Subject: NEC Questions


I have a couple of questions regrading the National Electrical Code:

1) Consider a power measuring device that is intended to be installed
into 
a residential 120V branch circuit, protected by a single 15 A or 20 A 
circuit breaker.  The device would be installed into a conduit outlet
box 
on the load side of the breaker to measure the power loads on the outlet

receptacles or lights connected to the branch circuit.  The device has
two 
neutral terminals with a 12 AWG copper wire connected between them to
sense 
the load currents.  This device would be wired in series with the
neutral 
(grounded) conductor for the branch circuit.  The live (ungrounded) 
conductor of the branch circuit would have a common connection on this
device.

Based on Section 300-13(b) of the NEC (NFPA 70), this device could not
be 
used in a multi-wire branch circuit, since the removal of the device
would 
interrupt the continuity of the grounded conductor.  However, I cannot
find 
any requirements that would prohibit the use of this device in a single 
phase branch circuit, protected by one circuit breaker.  Since the 
resistive loss in the neutral circuit through this device would be 
negligible, would this device comply with the NEC?

My guess is yes, that it meets the NEC code requirements for this branch

circuit.  Any comments?

2) Consider the same power measuring circuit installed into a direct 
plug-in (NEMA 5-15P) with a single outlet receptacle (NEMA 5-15R) or
into 
an outlet strip with a 16 AWG power cord with several outlet 
receptacles.  Assuming that the measuring circuit is provided with a 
suitable fuse for overcurrent protection, are the outlet receptacles 
required to be protected by a 15 A fuse or circuit breaker in the device
or 
can they rely on the circuit breaker for the branch circuit for
overcurrent 
protection?

The UL product standard for this device is UL 3111-1 (Electrical
Measuring 
and Test Equipment), which is harmonized with IEC 61010-1, requires an 
overcurrent protector to be fitted within the equipment for all devices 
connected to the mains supply (9.6.2). There are no US deviations in
this 
standard that would allow the circuit breaker to provide this
protection, 
so based on this I would assume that a 15 A circuit breaker of fuse
would 
be required for the NEMA 5-15R receptacles.  I would also assume that a
20 
A overcurrent protector would be required for a NEMA 5-20R outlet
receptacle.

However, the UL product standard for household appliances (UL 60335-1)
does 
have a US deviation to a similar requirement for overcurrent devices
(19.1, 
Note 2) that states the The PROTECTIVE DEVICE in the fixed wiring does
not 
provide the necessary protection.  However, the US deviation states
The 
circuit protection device is permitted to provide necessary 
protection.  If I am interpreting this correctly, a household appliance
in 
the USA could rely on the panel breaker for